Hi All,

We have a single 48/5000 multiplus 2, with ESS and 48V lifepo4 battery in a parallel grid connected system. Also 4kw PV direct to grid with an old school grid connected inverter. Currently we use the victron 100A current sensor connected directly to the multiPlus to drive the ESS instead of an ET112 grid meter connected to the Venus OS (raspi).

The system is working great.


I have 2 questions regarding this if anyone can help.

  1. We want to add a second Multiplus. Can we do so still using the current sensor connected to the master only. If so do we just configure the slave in the normal manner but leave the external sensor fitted box 'unchecked' ? - Or do we need to fit a meter (ET112) ?

  2. Because we are running the current set up using the external current sensor the system thinks it sits between the loads and the grid (see photo) and as such throws up a lot of L1 overload messages. I assume I can ignore these as the L1 does not actually pass through the MultiPlus.


Thanks for taking the time to read my post.

jetstram61 asked
pcbl answered ·

2 Answers

Nur Überschuss in den Akku laden?

Moin Moin,


ich habe folgendes System:


Multiplus 2

48V 105Ah LifePo4 Speicher

2x MPPT 100/20

ET340


ESS Assistent ist installiert und so eingestellt, dass der Zähler gegen 0 gehalten wird.


Anliegen:

Ich möchte, dass nur PV Überschuss in den Akku geladen wird.


Problem:

Akku min. SOC ist auf 10% eingestellt (diesen SOC hat die Batterie auch gerade)

Generiert die PV Anlage über die MPPT's nun z.b. 100W, werden diese genutzt um den Akku zu laden (bis ca. 14%).

Danach wird der Verbrauch am Zähler gen 0 gehalten (PV+Akku) bis der Akku wieder bei 10% angekommen ist - danach beginnt das Spiel von vorn.


Ist es möglich, dass nur PV Power für die Ladung genutzt wird, die über ist?

Beispiele (vereinfacht):

Soll:

PV generiert 100W, Hausverbrauch liegt bei 600W, Zähler geht runter auf 500W, Akku wird nicht geladen.

PV generiert 1200W, Hausverbrauch liegt bei 600W, Zähler wird mit 600W gen 0 geregelt und die übrigen 600W fließen in den Akku.


Danke und Grüße,

equi


equi asked
sierra answered ·

5 Answers

Multiplus II 48/5000 automatically dropping water heater in case of overload

I'm having an off-grid solar system installed (16x415W + 2 x MPPT 250/100 + Multiplus II 48/5000 + 2 x 5 kWH LiFePo4). I'm worried about overload condition and would like to have an automatic system that drops the water heater (2kW) off line if the 5000 kW inverter output is about the be exceeded.

My question is if the Multiplus II has some features that can be used to implement this or do I have to have this implemented without help from the Multiplus? Can the relay be programmed for this application?

nyholku asked
Rob Duthie commented ·

2 Answers

Parallel MultiPlus - Current Transformer

For an ESS system with Multiplus II units in parallel I wanted to use a CT Clamp instead of an ET112 meter to measure the grid. I saw a statement somewhere before, saying that this won't work, but I'm not sure why it won't work. Can anyone explain why an ET112 or similar is needed instead of a CT Clamp? Or can a CT be used, maybe I have the wrong information?

spudgun asked
pcbl answered ·

3 Answers

Multiplus-II + ET112 + Current Transformer

Hi

I have recently switched from the CT to the ET112 and noticed something odd

I have a Multiplus-II 3kva + ESS + 140Ah 48v Li-Ion + Batrium BMS (CAN-Bus) + Cerbo GX + PV on ACin

Everything is working fine expect I have noted the following oddity

I was uing the CT and could see the MP2 quickly adjusting to the PV lows and spikes during cloud movment and demands on the ACin during normal operation mode, but since switching to the ET112 I was able to see the MP2 is now really very slow at adjusting the inverter power output and charging, so much so that I can see 1.8Kw export happening from the battery when the sun comes out for 5+ seconds and importing while charging due to the cloud covering up the sun, this is very odd becasue with the CT it was super quick to change and keep the grid at Zero import or export.

I think because the metering has been moved to the Cerbo GX this now has to tell the MP2 to adjust I just wasnt expecting it to be so poor at controlling it with such a slow delay

Everything is working fine just really slow, I'm not runnign anything extera or doing anything extra with the cerbo gx, it is however in superuser mode running v2.52 (came out the same day the cable arrived to pulg in the ET112 so unsure if its a v2.52 related or just expected behavoiur) and i have node red connected to it, no perf issues though and only 1 flow (your charge at night flow) connected to it. Top is not showing any processes that would slow this device down.

Is this expected behaviour when using a ET112 or any Grid meter?

Regards

Mark Boys

Noisy Boysie asked
pcbl commented ·

2 Answers

Fuses and Earth of the DC side of 3-phase system

Hello, how to understand the "It is essential the negative battery terminal between the units is always connected. A fuse or circuit breaker is not allowed" in the Multi II Manual? The interconnection between the units is meant? The BMS in error case disconnects the minus pole of the battery by N-MOSFETs, there is no way to do it in other way. And the DC terminals of the Multis see no difference (except of the stray capacitance) which pole is disconnected. Is it correct to earth the plus pole of the battery and insert the fuse and the DC switch into the minus line which can be interrupted by the BMS anyway? Thanks.

Anton asked
Alexandra commented ·

2 Answers

PASSIVE ERROR - Problem to get communication started between Multiplus 2 GX and BYD B-Box BMS

Dear Forum,

hope you can get me some hints regarding the setup between BYD B-BOX (L3.5) BMS and Victron Multiplus II GX (3000er), which I bought new.

I recently bought the BYD B-BOX battery used from another user who had it running with a Victron Multiplus but now switched to PylonTech.

My setup is as following: MPPT SmartSolar DC connected to battery (short test: charging works, as indicated by the BYD battery (low rate white LED flash and battery voltages are in a reasonable range) and Multiplus GX connected to the battery.

[image]

Actually, I not have AC-IN connected to the grid nor the EM24 (my electrician will do that next week). Connection with SmartSolar via the VE.Bus worked very nicely. Also I follwoed the video instruction of Guy to setup the Victron for first Multiplus setup (setting to 500kBaud, DVCC, etc). I used a Typ A cable for the CAN between BMS and VE.CAN. I have an end plug / resistor on the VE.CAN as well.

Status message after reboot the Multiplus is: Not connected. In the BMS-CAN port i found following error message: Error-passive TEC:0 REC:128. Some Multiplus continues pushing packets. See the screen shot below:

[image]

Do you have any hints which root cause the error message may have?

Thanks for your support!

uksubs asked
Alexandra commented ·

3 Answers

MPPT smart solar not going into absorption

Hi, I have on off-grid system with 3x Pylontech US2000C batteries, Multiplus II GX 48/5000/70 and MPPT smart solar 250/100.

When I initially set up the system I hadn't changed the charging limits advised by Victron ie absorption 52V, float 51V through the VictronConnect App but had set the limits via the VE configure software Charger Settings tab.

I was getting high voltage alarms but the MPPT was going into absorption and float, and recording as such on the VictronConnect App.

I have since updated the settings in the VictronConnect app which has stopped the high voltage alarms but the MPPT now never goes into absorption or float.

Is this a problem and if so, how do I fix it?



kirs-ten-henson asked
kirs-ten-henson edited ·

1 Answer

Multiplus II Current Sensor position

Some help please.... Installed Multiplus-II in grid interactive config with non-essential loads on ACin and essential loads on ACout. Installed supplied AC Current Sensor on grid mains supply conductor to premises. The problem: On Venus GX system overview all consumption is displayed under 'Critical loads' with 'AC loads' zero (even though some non-essential loads are on and drawing power). When mains CB is tripped, non-essential loads on ACin are load-shedded (as they should) and the 'Critical loads' value reduces accordingly (still zero on 'AC loads' on overview. I presume I have missed a setting somewhere - usually do installations with ET112 - 1st time using Multiplus II. Any advice?

albert-vd-westhuizen asked
pcbl edited ·

3 Answers

Multiplus II im dreiphasigen Betrieb wie ins Hausnetz Einspeisen?

Hallo alle Zusammen,

Bin neu hier im Forum.

Ich komme lieber direkt zur Sache. Ich hab mich bereits durch tausende Forums gelesen und nie so richtig eine Antwort auf meine Fragen bekommen, deshalb stell ich hier mal mein Projekt zusammen:

Ich habe für unser Haus vor, eine 3 Phasen Nulleinspeisung mit 16 kW/h Speicher (48V) zu bauen. Also es soll ins Hausnetz direkt eingespeist werden aber nichts ins Stromnetz rausgehen. Dazu habe ich mir 3x den Victron Multi plus 2 mit 5000VA besorgt. GX soll ein Raspberry übernehmen. Als Speicher dienen 16x Lifepo4 320Ah Zellen mit Daly BMS im Eigenbau. Jetzt wäre die Frage des Anschlusses. Ich würde hinterm Stromzähler vom Netzbetreiber ein EM24 anschließen, danach eine parallele Abzweigung für die drei Wechselrichter. Ich hab mal grob einen Skizzenplan zur Veranschaulichung erstellt:

[image]

Würde dies genau so wie meine Vorstellungen funktionieren und wäre bei Stromausfall über die Wechselrichter das Haus trotzdem mit Strom versorgt? Und am Multiplus gibt es ja mehrere AC Anschlüsse, an welchen müsste ich anschließen?

Vielen Dank schonmal im Vorraus!

madmaxrs asked
madmaxrs answered ·

2 Answers

Bruit ventilateur Multiplus II

Hello les Victroniennes et les Victroniens :)

Apparemment il est normal que nos Multiplus II génèrent prés de 60db lorsque leurs ventilos se déclenchent, je trouve cela excessif mais Victron l'a voulu ainsi...

Autant dans une usine voire un container cela est jouable autant dans un espace clos non isolé phoniquement cela est TRES pénible.

De plus que les ventilateurs ne se déclenchent par avec une sonde de température mais lorsque la demande électrique dans un sens ou l'autre est importante et c'est dommage car dans un salle climatisée à 24° avec une température de 33° au sommet du Multi, les ventilos se déclenchent quand même...

Donc bouteille à la mer, une ou un d'entre vous aurait-il une idée pour diminuer drastiquement cette nuisance bien inutile sans devoir démonter le Multi, remplacer ces ventilos par des plus silencieux et ainsi perdre la garantie?

Bien à vous

Victronement vôtre :)

maa asked
dvb answered ·

7 Answers

Question pour mise en service Multiplus II + Cerbo GX + Pylontech

Bonjour à tous,

J'ai reçu mes câbles, je vais pouvoir mettre en route Multiplus II + Cerbo GX + Pylontech (il ne manque que le RS450/200 pas encore livré).

J'ai prévu cet ordre pour paramétrer l'ensemble, mais j'ai un doute. Est-ce OK ?

1) Tout mettre sous tension.

2) Paramétrer le Multiplus II via le câble usb-mk3.

3) Paramétrer le Cerbo GX (dont : capacité Pylontech + courant de charge + conditions de charge).

Vu que le Cerbo GX pilote tout, il y a forcément plein de paramètres du Multiplus II qui ne servent à rien, je ne sais pas si cela est visualisable ou pas. Je verrai :-)

Merci pour vos précisions.



dvb asked
sharpener commented ·

6 Answers

Do I need RCD protection on AC-In on Multiplus-II (UK based)

Hi,

I'm planning my installation of a Multiplus-II 5000/70/50 in my home in the UK along with ESS and later solar. I will be splitting my existing consumer unit into essential and non-essential loads to enable UPS mode in the event of a grid outage.

My question is whether the circuit protection device fitted inside the non-essential loads consumer unit which feeds the Multiplus-II AC-In input needs to have RCD protection or if an MCB can be used. Of course I will have a full set of RCBOs on the various other circuits on both essential and non-essential consumer units but I'm concerned about discrimination if I was to also use an RCBO to feed the Multiplus-II input. I could probably get a time-delayed RCBO but I wonder if this is really needed.

The Multiplus-II installation manual simply states that

The AC input must be protected by a fuse or magnetic circuit breaker rated at 32 A (for 3 kVA model), 50 A (for 5 kVA model) and 100 A (for 8 kVA and 10 kVA model) or less, and cable cross-section must be sized accordingly.

so my guess is that this might not be so much an inverter product question but more of a UK wiring regs question.

I have the regs and on-site guide so can read up on that but just wondering what others have done? The cable feeding Ac-In will be 10mm2 (singles ideally but T&E possibly) and will be running a short distance through 75x75mm trunking to the AC isolator and then again in the same trunking to the Multiplus-II so risk of damage to the cable is minimal. I could use SWA but that would be cumbersome and probably overkill.

Any thoughts? My feeling is that using a 50A MCB is the pragmatic choice but I'll need to check the regs to see if the short run of non RCD protected cables in trunking is a problem.

Thanks, Craig.


Update: Checked the OSG in section 7.2.5 and as far as understand it, as long as the cables are not “installed in walls or partitions”, which surface mounted trunking isn’t, there is no requirement for RCD protection. The prospective fault current in a fault condition inside the Multiplus would easily cause disconnection of the 50A MCB inside the allowed time so I think an MCB is appropriate. Anyone aware of any other regs which contradict this or am I misunderstanding anything?

craigc asked
sharpener edited ·

1 Answer

Multiplus 2 schießt den Generator ab

Hallo

Bin gerade am Aufbau einer Notstromanlage mit anschließender Erweiterung mit 9PV Modulen und einem Fronius auf AC out1

im Moment vorhanden und angeschlossen

Multiplus 2 5000 GX

3x Pylontech 2000

einem Inverter Generator von Hyundai mit 4500va

Ich möchte das Setup möglichst so einstellen dass es im Vollausbau funktioniert.

desshalb habe ich das ess eingeschaltet,und das Ländernetz für Austria.

Im Moment ist die Anlage vom Netz getrennt und wird mittels Umschalter,entweder Netz oder Multi,auf die Hausinst. geschaltet.Wie gesagt ich bin erst am Anfang.

Nun zum Problem

Pylons sind halb voll,Netz ist weg ,ich schalte um auf Notstrom

Multi versorgt Haus von der Batt.

funktioniert!

jetzt schalte ich den Generator ein.

funktioniert im Prinzip wenn ich das mit angeschloßenem Pc und Mk3,und Veconfig mache,denn dann trennt der Multi die Verbindung von der Batt und somit Haus stromlos.

nachdem der Multi aufgeschalten hat und ich das Mk3 abziehe dauert es ein paar sec

und der Multi versorgt das Haus und ladet die Batt.

Mache ich das ohne Mk3 versorgt der Multi das Haus weiterhin ,nur sobald er den Generator durchschaltet, geht dieser in Overload und schaltet aus.

Last am Ausgang 200w,Ladeleistung 1200w wobei wenns funktioniert steigert der Multi die Ladeleistung von 0 weg bis eben 1200.

machmal funktioniert es sogar ohne Mk3 ,aber eben sehr selten.

Meine Vermutung ,beim aufsynchronisieren entsteht ein kurzer Impuls der den Gen abschießt,wenn Ac-out mit AC-in synchronisiert ?

Gibt es eine Möglichkeit den Generator vor diesem kurzen Ereignis zu schützen ?


danke

L.G.

Manfred














prima asked

0 Answers

Multiplus 2 keine Synchronisierung

[image]



Mein System

Cerbo GX

Multiplus 2 5000

Seplos BMS mit 16x 280ah Akkus

EM24

Solar Edge Wechselrichter mit 7,83 kwp (ist aber noch nicht mit dem Cerbo verbunden.


Nun folgendes Problem. Wenn der Multiplus aus ist, wird mein Grid am Netz Eingang richtig angezeigt.


Sobald mein Victron Läd oder entläd wird die Netzseite nicht mehr erkannt/ignoriert

Beim Entladen geht der Multiplus in Bulk und die Main Lampe Blinkt. Die entlade Lampe leuchtet grün.

Laut Anleitung Synchronisiert der Multi nicht und trennt daher das Netz, die Frage ist warum Synchronisiert er nicht ? Hat da jemand eine Idee ?