There seems te be a problem with the data comming from the et340 grid meters that we have installed for multiple clients and they are all acting strange.
The Total grid value is fluctuating a lot and it is forcing the batteries to go into charge and discharge all the time. The Ess phase compensation for a single multiplus2 in a three phase grid was working before and it reacted to the values from the grid meter, only problem is that these now go from minus to positive in 5sec and forces the ess to change constantly. Is there a problem with the meter, rs485 connection or do we need a current transformer to get these readings correct?
All firmware updates have been done to latest version and still no changes.
0 Answers
Today I was testing my system an realise that there was 115v between L and earth and same between N and earth…
But only when I use the CA input rules, (when CA in is disconnected) is it normal I thought it would cut only N and L not the earth…
How can I deal with that, put and other earth cable ?
1 Answer
We have a weak 3 phase diesel genset what suffers from asymmetric 3 phase loads. According the 1:1 rule, there are 3 MP2 in star connection with sufficient power to complement missing loads with battery charge currents. Assume, the setup requires any electricity meter (our dealer has ABB on stock) with RS485 at generator output, how can I setup the MP2 to balance the phases over the batteries DC busbar ?
1 Answer
What is the condition that the Multiplus II 2x120 uses to determine its power flow as described in the Data sheet? Or whether the AC input is 120v or 120v/240v split phase?
[image]
In the case of the Multiplus II 2x120, when you connect the inverter in-between the automatic transfer switch and the RV panel the 120v/240v input connection works as intended and a 120v input connection also works as intended. Unfortunately it seems that the Multiplus does not pass through both lines from industry standard generators.
[image]
I believe the problem is that a lot of RV and off grid generators only output 120v. Most of them such as the Cummings Onan- 5.5HGJAB-6755L which is rated for 5500watts or 45+amps has two outputs. Each is 120v and outputs about 23amps. In most cases it is not possible to combine L1 and L2 out of the generator as the two lines are out of phase, not 180° out which would give you 240v but 120°. Meaning you can't combine the 2 lines to get the full 5500watts or 45+amps single phase to the Multiplus. Probably a cost savings thing on the part of the generator manufacturer as they can use the same components across multiple generator configurations. Either way this is common place in the industry here in the US.
So my question is, can the Multiplus II 2x120 be configured to detect this power type and passthrough both legs? If the Multiplus is actually detecting the phase and not just 240volts then there should be reason to believe Victron could remedy this with a firmware update. Correct? Also, if the voltage between L1 and L2 is 208v would that be an easier setting than the phase detection?
5 Answers
I am putting together a dual phase system using 2x 48/10000 Multiplus II for a client who is supplied 3 phase from grid, but only uses 2 of the phases. When commissioning, what phase angle would be required?
1 Answer
Hello,
Is it possible to install a MultiPlus-II 48/3000/35-32 combined with a single phase PV and Battery on only one phase of a 3-phase-grid house system? Target: Reduce cost compared to a 3-phase-system, but still have a backup in case of grid power loss. All the critical loads in the house are connected to that one phase. There are no specific 3-phase-loads in the house used.
I ask, since so far I've not seen in any description duch a system design...Thanks for any advice!
1 Answer
We have connected a three phase 5KVA multiplus-II system.
the inverters are updated, now we want to configure them, we doing so without wiring the AC in but with the 480V battery wired up.
when we switch on the first one its ok but when the second one is switched on it starts beeping and the "absorption LED" lights up same with the third inverter, and we get error code 3.
Any assistance will be appreciated.
2 Answers
Can anyone assist me with this, I think I'm missing something.
We wired and configured successfully a three phase multiplus 5KVA inverter. When it's switched off and using a multimeter reading ACout 2 between L1& L2 (lines) I'm getting a short is this normal?
When we switch it on and reading between L1 & N (phases) I'm getting the 230 which is acceptable.
3 Answers
Can anyone assist me with this, I think I'm missing something.
We wired and configured successfully a three phase multiplus 5KVA inverter. When it's switched off and using a multimeter reading ACout 2 between L1& L2 (lines) I'm getting a short is this normal?
When we switch it on and reading between L1 & N (phases) I'm getting the 230 which is acceptable.
1 Answer
Hi. I have a small farm in which I have various pumps, biggest one for now is 4.5Kw. I also have a house nearby and I'm considering getting a solar system given the provoked .....Erm, sorry I mean the current energy crisis... :) Anyway, all the pumps are 3 phase, the house is single phase. My initial thoughts were to get 3 Multipluses 3000 48 and set them in 3 phase, but then I remembered that I'd have to be very carefull because of a water heater and oven in the house, that together surely surpass the MP's 2400W rating. Now I found about 2 companies that sell transformers to the industry and they have 3phase to 1 phase converter tranformers and also vice versa!! For 5Kw those things weight more than 50Kgs !! But they cost about 2/3 of a single new MP.
The other option , which I'm pending to right now, is to get a single higher wattage MP (i.e. the 8000 48 version or even the 10000, although that is probably overkill and has too much losses for my taste, was thinking of minimizing the battery size for now) and put a single to 3 phase converter transformer in the circuit for the pumps.
Question is, which one would be preferable ? I know using transformers to make the conversion, one way or another, is going to incur in losses, does anyone have any experience with this ? The companies do provide a datasheet but they don't include the efficiency and why should I trust them for that anyway, the efficiencies for transformers are probably known in general.... Here is a link with an example: https://www.torytrans.com/en/transformers/phase-converter/single-to-three-phase-converter-transformers-ip23
Going with a single MP would be better in terms of future maintenance / repairs / replacement (although this shouldn't be a factor with Victron, given the higher quality, but eventually anything can die), given that if I have 3 MP wired for 3 phase and one of them goes wrong, I'd have to find a replacement with exactly the same model, whereas with a single bigger one I could borrow one / have a spare / more easily...
One advantage however if I go the path of 3MP wired in 3 phase is if one inverter malfunctions I would
still have the other two to feed the single phase circuits in the house, and could even wire it in parallel with the other one.
Decisions ....
But yeah, I'd like to know the potential transformer losses of the phase converter transformers and if anyone has any experience with this...
Also, another option would be 3 MPs wired for 3 phase and a separate MP for the house, no transformer losses then, although it's more expensive... In this case I could also go with smaller MPs for the 3 phase wiring...
What do you guys suggest ?
Thanks a lot!
2 Answers
Hi,
I have a single phase off grid system on an MPII 5KVA using the SOC generator function to switch via ATS to the distribution network (I don't use it as a generator!!! If the PV is disconnected (SOC) the whole system is connected to the distribution network. "Please don't confuse this with a generator" ). I am satisfied with this solution.
But I would like to increase the 1 phase power from 20A to 40A by parallel wiring and keep the wiring I have (if possible). In the prospect documentation it is written that it is possible to connect up to 6 pieces of MP-II (parallel). Honestly, I'm not quite sure how to connect it :) So maybe you can guide me if I'm doing it right...
---
Question about connecting two pieces of MPII in parallel (one phase):
a) From MPII (Slave) AC OUT1 I bring the cables to MPII (Master) AC IN, since I do not use the distribution network via victron (we don't have to solve why).
b) Or MPII (Master) AC out I will send the cable to MPII (Slave) AC In - but here I have a feeling that the Master-Slave logic will change :)
How to actually wire it properly???
--
If I'm not mistaken, I have two options to connect and configure?
1) is a generator where additional MPii are connected from a certain load
2) parallel phasing - this seems like a more reasonable solution to me, but I haven't been able to find out how it works in practice yet.
Regarding the following configuration (ve.config), I found something regarding parallel connection via ve.config. I will document later.
Thanks for advice.
1 Answer
Situation: 3p configuration of 3 Multiplus or Quattro devices.
Everything works fine, until it doesn't. Now one of them goes kaboom for internal reasons (i.e. device failure).
As soon as that happens, the whole system goes down "of course". Now the question is, how does one proceed to restore at least partial operation until the faulty device comes back from repair. Two phases could work which is better than 0 phases.
Assume the faulty device has been taken offline, and there are 2 - potentially working - devices left. until the faulty device is sent back, repaired and sent back-back it will take a week. What now?
Configure the remaining 2 Multis for parallel configuration is not going to cut it as they have different AC Outs - yes/no?
Simply turning off "switch as group" will also not cut it, because there still is one missing for a 3p config?
Reconfigure for 2p operation?
Is there a manual how to proceed for these cases?
2 Answers
Hello everyone, I,m new at Victron community and I,d like your help in a photovoltaic project which I,m dealing.
I,m taking some online training at Victron professional and I guess I,m learning, But I would like to share my case to hear yours opinions
I need a 3 phase off grid system with a ESS (30kwh possibly to up to 60kwh), to be installed at a single home. I understand that a gasoil/gasoline generator will be needed in case of emergency.
The AC loads could be around 40-60 kWh/day, and the peak consumption around 10 kw.
The power of solar panels installed around 18 kw.
A future conexión to the grid is possible.
I would like to hear your opinion about the best efficient system, (with newest Victron equipment actually) Thank you very much.
2 Answers
Hi dear Victron community!
I have a grid connected three phase AC-out-coupled system with Multiplus-II, CerboGX, SmartShunt, Lynx distributor and battery balancers. Battery pack is 48V 600Ah made from 12 pcs of 12V lead acid GEL batteries (picture below).
[image]
I would like to connect a back-up generator for the wintertime to help the batteries when the electricity price is really high and the SOC is getting low. There is three possible solutions in my mind.
1. Generator and changover switch to AC in of MPII. That needs a very powerful 3-phase generator which is expensive and there are troubles with feed-in.
2. Generator and Skylla charger to the DC side. Not a big generator needed but there is no VE.bus communication with the system.
3. Generator and another Multiplus (preferred). This way I could have intelligent communication, more flexibility and even one extra 1 phase output from the extra Multiplus. Is it possible and logical this way? Red colour is for new equipment. Is there anything else I should add (generator auto start for sure)?
[image]
Any ideas, suggestions or examples are welcome...
Karl
5 Answers
Ok I will try to be as clear as I can.
I have 2 multiplus 12/3000/120 in a split phase config.
10 100ah Battle born lithium batteries with a shunt in two separate (5 qty ea) battery banks routed and fused to a single 1000amp terminal block
Battery Cabling is 4/0 Windy Nation and I will admit it is on the outer limits of length.
Inverter Cabling is 2/0 Windy Nation X2 from inverters to same 1000amp terminal blocks noted above.
AC units have softstarts but are already running at the time of the outage
The inverters will handle both AC units for many hours if I shut them down first then transfer power to the inverters and then turn the AC units back on. So they are absorbing the in rush from the compressors nicely just won't transfer it.
Problem: Inverter will not ups a 10-14 amp load on either or both inverters. If I am running say a 1000 watts or less there is no issue.
Observation: In VRM downloads I can't find anywhere the battery voltage dropped too low or the temps on the inverters at the time of the outage was 38C so according to specs should be able to handle 2200w each, no DC ripple, nothing I can see for the inverter to shut down.
Question 1: What else might cause this shut down. Could cabling being at the edge of acceptable lengths cause this but not show any indication of a cut off in VRM
0 Answers