Can I use a common busbar for the neutral wire of AC OUT1 and AC OUT2? In the diagram they seem to be connected inside the multiplus 2.
I have parts of my home wiring sharing the neutral wire but I want some loads to be supported by battery and some not in case of outage.
AC IN neutral will be separate.
Thanks
3 Answers
Bonjour à tous et toutes, je souhaite installer dans un avenir proche, une borne de recharge EV Victron. Je possède un Multiplus II 48V/10 000VA J'aimerai (pour des questions de facilité de raccordement) alimenter la borne de recharge sur la sortie AC OUT 2 de mon Multiplus II. Je veux pouvoir recharger mon véhicule en journée grâce à ma production solaire, mais également de nuit (en ponctionnant sur mon parc batteries de 20K en Pylontech, durant quelques heures). Cela est-il possible de programmer le Multiplus II pour que la sortie AC OUT 2 se comporte comme je le souhaite ? Cordialement.
2 Answers
AC-out-1 works and the batteries are charging however while charging in bulk the AC-out-2 stays off.
2 Answers
It is my understanding that AC2 can be utilised for non-essential loads and given that surplus PV output is available, the surplus can feed these non-essential loads when grid supply is present. My question is if there is a limit on the current through AC2? Could I, for example, connect a potential 20A load on AC2, such a water heater in addition to a 15A essential load on AC1?
1 Answer
MP2 48/5000/70 - GX
I have some original Enphase m215 micro-inverters connected to AC-out-1 which I manually switch on and off to prevent the m215's pushing the voltage too high when the batteries are fully charged. I have tried setting the PV inverter assistant, but I think the m215's are so old they cannot limit their output on frequency shift.
As this whole system is off grid I would like to connect the m215's to the currently unused AC-out-2. I would like to know if I can configure the internal relay which switches AC-out-2 on/off depending on the grid being detected at AC-in-1, so that it switches on/off based on battery SOC.
Any advice would me much appreciated.
2 Answers
AC Output #2 on the Multiplus 24/3000/70 shuts off when the batteries are charging. We are using the Multiplus in an off grid system for household power. It doesn't appear that can be changed. Does this apply to the Multiplus 2 or is AC Output #2 hot continuously as is #1?
1 Answer
Hello all I am wondering if there is a setting using the programmable relay or other relays in the inverter that can be helpful to do so :
bypassing the AC input 1 to the loads those are connected to AC out 1 & 2 in case the inverter fails or shutdowns due to some errors.
1 Answer
I'm looking for recommendations on 125A/240VAC two pole RCD/GFCI breakers. It seems while ASI produces 125A breakers they stop at 63A for GFCI protection. I am in the South East US.
I see lots of mention in the forums about using a RCD but never a specific brand/name in conjunction with the Quattro 10ks.
0 Answers
Hi there
I have a multiplus 3000/230v and I do not manage to get any voltage on the AC Out 2 when connected to the grid.
Is there any magic to get this to work??
cheers
3 Answers
hi all,weve got a pheonix smart 24/3000 inverter, just wondering what size cable to get for the AC output, in the manual is says 26a short circuit output i cant see any other mention of AC output, also the output screw terminals arent very big so i doubt if cable bigger than 10mm2 would fit, thoughts from anyone who has this inverter
1 Answer
Hi team,
I am looking into a strange item. The Quatro is connected to shore power and to a generator, the AC1 is going to my ship and I planed to use AC2 for the watermaker and heater.
All is setup and I can use the AC1 output. But I do not see the AC2 output.
I do not have the interface but I have a GX connected to the victron network.
How can I activate the AC2 and set limits to the input? or is this AC2 broken and should it always be activated? or is it only working when AC2 input is there and not AC1 input...
Thanks
3 Answers
I have an AC inverter connected to AC-Out-2 on a MultiPlus-ll.
A generator is going to be connected to AC-In-1
I would like to turn AC-Out-2 off when AC-In-1 is active and when Aux-Input-2 is open due to a BMS high battery voltage signal.
AC-Out-2 turns off when AC-In-1 is active but AC-Out-2 will not turn off when Aux-2 (BMS high) is open because it is still being driven to stay on by AC-In-1 not being active.
The idea of this is to avoid using a contactor on the AC inverter.
Can these two be done in combination?
Hopefully makes sense!
1 Answer
Dear experts,
I'm using a 48V solar system in an area where there is sometimes grid power. Because in general my solar capacity is sufficient for my loads, I set the virtual switch of my Multiplus to only charge when the voltage of the batteries drops under 50.0V. Unfortunately AC-out 2 appears to be dependent on the same AC input relay and cuts the power when AC-in is ignored through the virtual switch. However, I would like to be able to use my AC-in via AC-out 2, for certain equipment, while not charging the batteries. Is there a way to program the Multiplus for this or should I just make a bypass of the AC-in before it enters the Multiplus?
Kind regards,
Mark
3 Answers
Hi,
I'm configuring a system with 3 MP2 , in a 3 Phase out setup. As per the instruction video's etc. this should not be any problem, but the charging doesn't start when the phase comes up at the master L1. The 3 phase out put works fine.
So I have checked the forum, and checked the training video's again.
In the training video's its shown in the following diagram. The inputs of L2/L3 are seemingly connected with a 0V, therefor I tried to have the null connected to all three inputs, this didn't help.
[image]
Anybody an idea what I have done wrong? Are the connected nulls at input needed (electronically I can't imagine it's needed, but the screenshot shows something there)?
Best regards,
Emiel
2 Answers
Hello,
I have 2x EasySolars 24/3000 (basicaly Multipluses) configured in parallel.
The problem is that from time to time the main ac-our breaker tripps (one or the other inverter). How can I identify the issue?
Seems sporadic to me with no special events..
Thank you!