andy-2xs avatar image
andy-2xs asked
SoC incorrect onQuattro/Cerbo/Smartshunt
SoC on discharge is dropping approx 2x actual based on AHrs consumed. A, V & W all reporting correctly.
This is a new install comprising 24V AGM + Quattro + Smartshunt + Cerbo. Cerbo connected to Quattro via VE Bus and to Smartshunt via VE Direct.
The Cerbo however is powered from a 12V source - could this be causing the incorrect SoC reading?
Thanks for any suggestions.
MultiPlus Quattro Inverter Chargercerbo gxSmartShuntSOC
JohnC avatar image
JohnC answered ·
Hi @Andy-2XS
SOC isn't actually designed to match Ah discharged. The Peukert Exponent sees to that. Though your "2x" would indicate a very heavy load at the default 1.25.
For testing, try setting Peukert to 1.0 at a reasonable discharge level. This will actually show on VictronConnect (probably elsewhere too) as a change to SOC in realtime. You can then reverse that with no effect on the data. Bear in mind that Ah isn't a true measure of energy in itself, but it should get much closer to matching.
I doubt the Cerbo has anything to do with it. Try that little test to see, and perhaps record the temporary change on a VC Trends graph so we've something to work from.
andy-2xs avatar image andy-2xs commented ·
Thanks John!