bivaccamper avatar image
bivaccamper asked
Genset draws current while running ????
Yesterday I went to help a guy with a Victron installation:
- 3x Multiplus 48 5000 in 3-phase configuration
- 1x Color Control
- 1x Smart Solar 250 / 100
- 1x 13.8 BYD battery
- 1x 9 KVA 3-phase genset
I've set up the system (multi, mppt and color control and autostart for the genset by low SOC)
First I've found a problem that whith the genset on, the multis read voltage at the input but not charging, just inverting.
We found that rotating 1 input phase solve the problem.
The funny thing is that when the genset is charging, the color control shows it as a AC INPUT, but also as an AC LOAD.
If I stop the genset the loads disappear (also the input)
Is like the genset draws current.
Can someone explain that? It's fixable?
Thanks
MultiPlus Quattro Inverter ChargerCCGX Color ControlGeneratorgensetgenset multiplus
Johannes Boonstra (Victron Energy Staff) avatar image
Johannes Boonstra (Victron Energy Staff) answered ·
In a Multi /Quattro the AC out is not measured but calculated using AC in and the the DC current.
So it can be due to a measure error/power factor or such that this value is incorrect, resulting in these ghost values on the CCGX display.