Hi is it possible to run 1 Multiplus 48/3000/35 and 2 x Phoenix 48/3000 inverters in Parallel? where the Multiplus and a SmartSolar MPPT 250/100 is used to charge the battery bank and the Multiplus and Phoenix inverters supply the peak AC loads.

Thanks,

Jannie

Phoenix InverterparallelAssistantsconfig
10 |3000 characters needed characters left characters exceeded

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
WKirby avatar image
WKirby answered ·

Howsit.

All VE.Bus devices to be used in a parallel or three phase / split phase configuration need to be on exactly the same firmware.
Multiplus and Phoenix inverters will have different firmware numbers.


1 comment Share
10 |3000 characters needed characters left characters exceeded

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Check that, I found that Phoenix inverters are fitted with Multi chips.

You still need the same chip firmware though.