Generator Stop after Grid is available

System:

Two Quattros - setup in SplitPhase

ACin1 has a generator

ACin2 has the grid

Four MPPT Solar controllers with a total of 56 panels

Large Battery managed by internal BMS that communicates with Venus.


Venus configures:

ESS Configured

Generator Start when SOC is at 45%

Generator Stop when SOC is at 90%


Should buy from grid if it SOC falls under 50%,

Should charge Battery with solar


The problem: during the night time if the system gets to under SOC 45% because of grid failure, the system turns on the generator, if a few minutes later grid is available, it does not shutoff the generator. In my case an hour later I had plenty of sun to charge the battery. I have not been able to tell the system to prefer the use of grid over generator.


Is there a way to fix this?


-Carlo

Venus OSGeneratorSOCgrid
2 |3000 characters needed characters left characters exceeded

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
Alexandra avatar image
Alexandra answered ·

You can program in quiet hours to prevent the generator starting up near the time you know you will have pv soon.

https://www.victronenergy.com/live/ccgx:generator_start_stop