jimmymcknife avatar image
jimmymcknife asked
Quattro charger switching off every few minutes
I have a Quattro 24v 8000 as part of a 4kw off grid solar system with 1000ah traction batteries (12 x 2v in series) . I have a Hyundai DHY8000SELR generator (apparently 7.2 kva) wired into the AC1 of the quattro. I have set the input voltage to a maximum of 16a as my generator seems to trip out if its set above this (which is annoying as it should be able to provide 30a, but this is a separate problem).
The issue is that the quattro is switching to charging (bulk) and mains staying in this mode for a couple of minutes then switching back to inverter mode for about 20 - 30 seconds then back into charge mode. Is there a reason for this? have I got the settings wrong?
Any help/suggestions would be really gratefully received!
I've also set with the dip switches the charge current limitation to 75%
so the dip switches are as follows:
8= off
7= on
6= on
5= off
4= on
3= off
2= off
1= off
battery chargingoffgridinverter current drawHelp
There is quite a complete set of settings adjustments to improve generator reliability here :
https://www.victronenergy.com/live/multiplus_faq
Please read that, and try those. It has a very high success rate when followed.
Victron Offgrid page
VictronConnect VE.Bus charging manual