Multiplus II PMP482305010 rev 08 and rev 09 parallel compatibility

Hello!, are the 08 and 09 hardware revision of the PMP482305010 fully compatible for a parallel setup?

Best regards.

Multiplus-IIbattery charging
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

2 Answers
Guy Stewart (Victron Community Manager) avatar image
Guy Stewart (Victron Community Manager) answered ·

Hello @Alfredo,

I have confirmed that it is possible to use these two models together in a parallel and three phase system.

The software checks for the first 4 digits in the firmware number (in this case 2629), if that number changes, we also typically will change the part number, (PMP482305010).

3 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Warwick Bruce Chapman avatar image Warwick Bruce Chapman commented ·

@Guy Stewart (Victron Community Manager), there seems to be an inconsistency in the document http://www.victronenergy.com/upload/documents/manual-VE.Bus-firmware-versions-explained-EN.pdf.


I note that it has been edited in 2020 to indicate clarification of this paragraph. As it stands, the example table says this is possibly even if the first two numbers differ but as long as the model and firmware version matches:

1606160955777.png

Example you could use a combination of:

- 2641 Quattro 24/3000/70-50/30

- 1941 Quattro 24/3000/70-50/30

As long as you used only the newest firmware available in the 200 series since the 400 series is not available on the 19xx microprocessor.

Thus, it would be 2641209.vff and 1941209.vff as a the time of this post.

1 Like 1 ·
1606160955777.png (28.5 KiB)
alfredo avatar image alfredo commented ·
  1. Ok, thank you so much!, I prefer you to confirm, but reading Victron website:
  • All units in one system must be the same type and firmware version, this includes same size, system voltage, and feature set. The type is indicated by the first four digits of the firmware version number. For details, see the “VE.Bus Firmware Numbering System” section in the VE.Bus Firmware versions explained document.


Both of them are same model PMP482305010 and have identical firmware version 2629.

Them only differs on hardware revision: hw rev 8 and 9.

Best regards.




0 Likes 0 ·
alfredo avatar image alfredo commented ·

Great!, thank you so much Guy.

0 Likes 0 ·
Robert Boerescu avatar image
Robert Boerescu answered ·

I have an easysolar 2 and in remote console shows like:

1685528453103.png


Is the product id the info I need to get a compatible MP2 for parallel or three phase system?

Thanks!



1685528453103.png (26.9 KiB)
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Related Resources

MultiPlus-II Product page 

MultiPlus-II Manual

MultiPlus-II 230V Datasheet 

VE.Bus Error codes

Additional resources still need to be added for this topic