ebrahim@brighthousesolar.co.za avatar image
Why - 3 x Multiplus II 48V - High Peak Output Current not Equal to Input Current
System 3 x Multiplus II 3kW 48v in Parallel with 2 x 4kWH 52v Blue Nova
Purely backup systemAC Output Current 33.6 AAC Input Current 15.2 A
AC Output Power 688W
Battery -2.60 A 55.65 V
System in Float
No Warnings or Alarms
1) I need to make sense of the above.
2) Installation - Trips 40 A Output Breaker on essential loads.
3) System sometimes shuts down - Overload - when ( No mains Available )
Please Assist, Thanks Ebrahim, Cape Town, South Africa.
Multiplus-IIparallel
JohnC avatar image
JohnC answered ·
Hi @ebrahim@brighthousesolar.co.za
Those VRM graphs are per-minute, and only reporting a reading at that particular instant. And depending on the sampling time of each input, may not match, nor balance. So it's hard to relate to a breaker trip issue happening a second (or mS) later by VRM-reported values.
Alarms, either on GX or VRM, need to be set up. VRM will even email them. You may well have a breaker overload issue, but this data/alarms aren't set to show you that..
Unless your breaker is faulty, you likely have a real overload issue. Detecting it is another thing..