EasySolar II GX, Cerbo, 4x Pylontech US5000.
CCL set to 200A, was set by Pylontech to 80A. VRM still displays 80A
EasySolar II GX, Cerbo, 4x Pylontech US5000.
CCL set to 200A, was set by Pylontech to 80A. VRM still displays 80A
Hi @kevgermany,
This is expected behaviour.
The advanced widget you're looking at in VRM sources its data from the battery BMS. Additional limits set elsewhere (like a custom DVCC setting) won't affect the data shown there.
In this case as well, because the limit set by the battery is less than the 200A you have set manually, the system will not override the battery BMS.
To add, DVCC is not an override. The system honours the lowest of any two limits.
There are values from shunts but not what I'm looking for...
Thanks. New to this side of things. I saw the limit changed during the day. So the batteries appear to be setting a current limit depending on SOC maybe more.
Cleverer than I thought.