terror-storm avatar image
terror-storm asked
Error code: #67 - No BMS, Inverter turns off
We have an RV with a Lithionics 48V RV-C lithium battery & BMS (fw v9.0.02), Cerbo GX (fw v2.94), Multiplus II 3kW (fw 492), SmartSolar 150/35 (fw v1.61).
Periodically the system experiences an error with these symptoms:
  • The MPPT appears to lose communication with the battery
    • It changes from Ext. Control to Float, and produces code #67
  • The inverter AC output turns off
    • The VE.Bus state changes from Inverting to Off
It seems to only occur during the times 7am - 9pm, never after 9p or before 7a. Perhaps it has to do with the solar cycle? In my mind this is not likely a wiring issue, since it doesn't occur overnight.
The issue has always been rectified automatically in a short period of time (1s to 1m, 41s).
See table below for instances of the error, and snips from VRM showing the other symptoms.
Any insight is welcome and appreciated. Thank you!
Device Triggered by Description Started at Cleared after
Solar Charger - Solar PV array [279]
Automatic monitoring
4/19/2023 13:27
19s
4/18/2023 18:18
11s
4/16/2023 9:50
1m, 3s
4/15/2023 14:42
55s
4/15/2023 13:52
1m, 5s
4/14/2023 16:39
50s
4/13/2023 18:07
1m, 6s
4/9/2023 7:14
59s
4/8/2023 12:15
56s
4/6/2023 16:46
1m, 41s
4/6/2023 15:32
59s
4/4/2023 8:08
1s
3/28/2023 13:23
3s
3/27/2023 17:13
11s
3/23/2023 12:20
47s
3/1/2023 17:07
1m, 6s
2/28/2023 16:16
1s
2/26/2023 13:09
28s
2/25/2023 16:12
23s
2/20/2023 9:48
46s
2/19/2023 15:41
27s
2/18/2023 17:28
53s
2/18/2023 16:39
22s
2/17/2023 15:36
18s
2/17/2023 14:23
17s
2/16/2023 17:53
1m, 2s
2/13/2023 19:09
58s
2/13/2023 10:59
1m, 2s
2/12/2023 13:42
55s
2/7/2023 10:26
49s
2/6/2023 10:22
53s
2/5/2023 15:36
51s
Multiplus-IIcerbo gxLithium Batterysmart solar charging behaviour
derrick thomas avatar image
derrick thomas answered ·
Loss of communication to bms. Are you using a victron data cable between the bms and cerbo? Some aftermarket and diy data cables can be problematic.
terror-storm avatar image terror-storm commented ·
The Cerbo and BMS are connected to the overall RV-C network along with other devices. We are using an Ethernet cable for the Cerbo to interface into the network (with the end modified to connect to CAN), a cable from the BMS to the network (also modified), and a few UTP cables and connectors between the two.
Alexandra avatar image
Alexandra answered ·
@terror_storm
If it is happening during solar hours then maybe revise the voltages a bit. Maybe it is tripping and switching off. Hence the loss of comms.