de1nonly avatar image
de1nonly asked
Where can i find the Low Battery voltage setting?
I've got a system with 400ah of 48v LiFePo4 batteries and I'm constantly getting low battery Voltage warnings. But they seem to be set at 52.08 volts which seems a bit high.
I have an ESS running in Battery life mode. Images of setting below:
I can't for the life of me find the setting that is causing this alarm. Can anyone point me in the right direction?
Can I also get a sanity check on my settings? Including recommended settings for the DC Input Low Voltage Shutdown?
Lithium Batterylow battery warning48v battery
https://www.victronenergy.com/media/pg/Energy_Storage_System/en/configuration.html#UUID-7435bdda-8f3f-81c2-a1a6-dc8f1c9b2f8f
Your dynamic cut-off values are to high.
I would recommend to set all to 48V or 47V.
You also have to check the Inverter Tab.
de1nonly answered ·
Thank you, that was it!!! I had more reasonable values set in the Inverter tab but apparently it is overwritten when an ESS is running with the dynamic cut-off values.
Battery Compatibility