jagonzas asked

Multiplus II 48/1000 disconect fron grid with RoCoF too high msg (Grid code standar Spain)

Multiplus II disconnect from grid

Multiplus with grid connection on AC-IN, Fronius on AC-OUT and Pylontech bateries and Cerbo, all with latest firmware, with ESS assistant installed, Multi disconnect from utility grid, it you manually reconnected the grid, the system remain connected to grid for some minutes and disconnect again and every time.

error-victron.png


Gird Frec in is 50.1Hz Voltage around 240 (inside Spain regulation limits)

Any idea or solution?

Multiplus-IIgriderror
error-victron.png (87.0 KiB)
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

2 Answers
Meine_Energiewende avatar image
Meine_Energiewende answered ·

You seem to have a problem with your grid.

RoCoF means: Rate of Change of Frequency.

Jens

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

jagonzas avatar image
jagonzas answered ·

while it remains connected in mk3 alwais indicate 50.1Hz, no variation in VRM we can see:

freqmulti.png


so, despite the down in freq while disconnect it's look estable at 50.1, do you thought it's a Grid problem?? if we bypass the multi and reconnect grid to house, all run's smothly



freqmulti.png (12.6 KiB)
1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

jesper-zandin avatar image jesper-zandin commented ·
Do you still have this problem? I seem to be having the same issue and it would be nice with a solution.
0 Likes 0 ·