According to the Data Sheet and the manual a synchronised Parallel Operation with up to 25 devices connected via VE.Can is possible.
Is a 3 Phase system Setup also possible ?
According to the Data Sheet and the manual a synchronised Parallel Operation with up to 25 devices connected via VE.Can is possible.
Is a 3 Phase system Setup also possible ?
Hi, the Inverter RS can synchronise its (solar) charging.
but not its AC output. Not for parallel operation of the inverters, and not for three phase or split phase either
Some day it will, but not now.