Bernhard Matschinger avatar image
Bernhard Matschinger asked
Ground Relay Error 8 with Fronius IG Plus when switching back to grid
Hy All,
we deliverd a new Installation (Number 8) to an "existing" Farm House with a 3 - Phase ESS 15 kVA - Multiplus II System.
There is a Fronius IG-Plus 120-3 running for more than 12 years. So good for now.
Everything is working fine except we start the system in "Island" Mode with an Active IG-Plus. When AC Mains is connected, the System performs its Relais Test and after about 5 Minutes it is going to switch back to grid. Immediately, when switching back we get an Ground Relais Test Error 8.
When starting in Island Mode with a disconnected IG Plus everything is working fine.. after switching back to grid and connecting the IG Plus everything is working like a charm.
When coming from Grid with a GridLost, we also encounter the same problem when switching back to grid.
To make a conclusion.. When the Fronius IG-Plus is "Connected" (we switched off the system, because it starts working after 30 seconds.. so we could not test, if its a problem when standing by connected and producing), we get an Ground Relais Test Error when switching back to grid. (Always)
Whats wrong...
There is no mixed Ground and Netral (We have controlled that several times)
The Multis are showing those ERRORS:
Phase L1, device 1 (0) #44 0x820002
Phase L2, device 1 (0) #15 0x800024
Phase L3, device 1 (0) #19 0x800024
From the wiring...
AcMainSwitch - SwitchOverToGenerator - 100 mA 3 Phase FI - MulitplusII - FI-s to different Loads
the IG Plus is connected:
IG-Plus - LS 16A - FI- 003 A -To The MulitplusII Ac Out
As talking to Fronius Service Personal the have no Idea what s going on, because they say they do not connect Neutral to Ground ... so do we have issues with the 100 mA 3 Phase FI, or the FI 003A connected to the IG Plus?
The System is running the latest Firmware 487.
Unfortunately there is no Support from our Dealer, because they do not have the knowledge.
Have a nice day, always Sun and I hope to get some good feedback...
thank s in advance
Bernhard
Multiplus-IIFroniusgriderrorGrounding
Bernhard Matschinger avatar image Bernhard Matschinger commented ·
Answer to the above topic..
We did some "Hardware Solution" by disconnecting the Fronius completely with a 4 Pole NC Relay triggerd via Relay 1 on the Venus, triggerd by a small service written by me.. When there is no grid and it "comes back", we disconnect the Fronius, until the ESS had switched Back... After a Minute we connect the Fronius again;