Multiplus with two inverters, one on Output, one on Input.

I have two inverters. One (single Phase) is connected to the Multiplus Output. Measurement via Gavazzi EM24.

The Second one, 3 Phase is a Kaco, Connected to the grid. means Input of the Multiplus. (Modbus Sunspec and can be added via The PV Inverter Menu)

In the Menu the position is set to AC Input 1.

kacosdovnposdnbpdso.png

However, both inverters are combined in the schema. On the Output. multiplusiipvinvertertmsdvmsdov.png

With the 3Phase it is impossible, and I am wondering if all calculations will be made in correct way.

em24multplus 2 gxsunspec
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
klausbachmeier avatar image
klausbachmeier answered ·

The Screen can be fixed by setting "Grid Meter" to "external"

But this is not what i want. I'd prefer the measurement in the multiplus II instead of an external device.

Unfortuntly this leads to the https://community.victronenergy.com/questions/212778/wrong-values-in-vrm-with-ac-coupled-pv-inverter.html error in addition