question

matt23 avatar image

inverter off

I have a "3 phase" system running off 3 inverters, they charge the batteries from a generator. When I try charge from the generator the device says OFF but I can see the SOC and voltage both of which are fine. I also checked the gen voltage which is also fine. When I switch to charge only the CCGX the switches to fault.


Anyone know what this could be?

MultiPlus Quattro Inverter ChargerGeneratorfault
2 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Could you please post screenshots relating to your problems?

as you can see the inverter is switched on but not doing anything20210616-112012.jpg20210616-111915.jpg

1 Answer
Mike Dorsett avatar image
Mike Dorsett answered ·

Have you checked the phase rotation of the generator compared with the system? If the Generator rotation is 'backwards' it would show a fault.

1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Yes the phase rotation is correct and I can test at the inverter AC to see the the power is getting to the inverter. it clicks in and out every now and then but never charges