burnscraft avatar image
burnscraft asked
Split Phase System Configuration Advice
Need some advice on my setup please. The system consist of the following:
2- 48v 3kVA Quatros
50 amp 120/240 Split Phase Shore Power
7,500 Watt 60 Amp 120v Single Phase Generator
Cerbo and a bunch of solar ect...
The system is configured in 120/240 split phase with the shore power L1 going to the master Quatro AC-2 input and L2 going to the slave Quatro AC-2 input. The generator simply goes to AC-1 input on the master Quatro with nothing connected to the slave Quatro AC-1 input. This setup works fine but its a little lacking when running the generator when the batteries are low. I never see much more than 3,000 watts from the generator and the batteries don't see much of a charge when the slave Quatro has a load on it. This causes the generator to run hours on end not charging the batteries. Spending 12K on a new 240v split phase generator is out of the question. We need to keep the split phase for the 240v appliances onboard. Will a Victron auto transformer between the generator and inverters work for me? Or maybe two transformers so I can stack the inverters.. One after the shore power, 240v to 120v to stacked Quatros and then another transformer to get split phase off the Quatros. Any advice would be great thank you.
Lee
MultiPlus Quattro Inverter ChargerGeneratorAutotransformersplit phaseshorepower
Kevin Windrem avatar image
Kevin Windrem answered ·
I would do a 120v to 240v split phase autotransformer from the generator to the Quatro AC-2 inputs. Shore power to AC-1 inputs.
You could then also use the autotransformer for for 120 volt shore power to make 120/240 split phase.