dennis avatar image
dennis asked
Split Phase Setup in 3 Phase Network
Dear All,
is it possible to create a Split Phase System connected to a 3 Phase network?
First Multiplus 2 connected with AC in on Phase 2 and second Multiplus 2 connected with AC in to Phase 2. ESS with Feed Back enabled.
AC Out only of first Multiplus for some loads used.
All Neutrals connected like it is needed in manual.
Technically it should work, but is it considered by Victron Energy Software?
Thanks a lot!
Multiplus-II3 phase
chris-pt avatar image
chris-pt answered ·
Hello, did you try this configuration? It works? I would like to do the same... - Thanks for your return. Chris
Robert Boerescu avatar image
Robert Boerescu answered ·
I managed to do it yesterday. So far seems to be working as expected.
Kevin Windrem avatar image
Kevin Windrem answered ·
This was discussed in another thread also. One limitation: the Multis need to be connected to L1 and L2, not L2 and L3. You can see this in the Critical Loads tile above.