h-m-heating avatar image
h-m-heating asked
Mulitplus 24/5000 has 116v live AC out Neutral
One of our Multiplus 24/5000 Inverters has 116v on the Neutral AC output. This is without anything connected to the AC input and without anything connected to the AC Output so it is coming from the Inverter, I spoke to the suppliers who said that as long as the Inverter works OK then that is alright.
I don't agree that this should be left as clearly something is wrong with this Inverter and should be repaired, I would be interested in comments from Victron if they agree that it should be sent back for repair?
multiple inverters
seb71 avatar image
seb71 answered ·
Ground relay is on or off?
Do you have a PE wire connected?
5 comments
You forgot to ask the output voltage.
Sometimes it is best not to ask....
seb71 avatar image seb71 klim8skeptic ♦ ·
230V
Ur physic?
Multiplus 24/5000 is only 230V.
That is a fair point :D.
One would have to ask the OP,
h-m-heating answered ·
The output AC is 230v there is 111v between Neutral and Earth on the Output of the Inverter, yes we have a Ground PE connected to an Earth Rod and the Ground Relay box is ticked in the setup.