question

georgeleonardo avatar image

Inverter/Charger Setup - Moving from VE.Bus BMS to Smart BMS 12/100

Hello! My current setup is using a VE.Bus BMS and my MultiPlus Compact 12/2000/80 was configured to that. I remember I had to install an assistant for the VE.Bus BMS. I wonder what I'll need to do now. Should I uninstall the assistant? Do I need to do something at all? Thanks!

Phoenix InverterBMSmultiplus ve.bus
1 comment
2 |3000 characters needed characters left characters exceeded

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Still looking for this if anyone have any thoughts
2 Answers
Matthias Lange - DE avatar image
Matthias Lange - DE answered ·

Without the VE.Bus BMS you have to delete the VE.Bus BMS assistant.
But you then have to use the "two-signal-BMS" assistant.

https://www.victronenergy.com/media/pg/Smart_BMS_CL_12-100/en/appendix.html#UUID-98591649-4b54-ae3f-8f37-f2061c26b76c

6. MultiPlus 500VA – 1600VA & MultiPlus Compact 800VA – 2kVA

2 |3000 characters needed characters left characters exceeded

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

georgeleonardo avatar image
georgeleonardo answered ·

Oh that’s super helpful thanks so much!!