zapp999 asked

Phoenix 12/375 not showing any load in the app

I use Phoenix 12/375, together with VictronConnect. VictronConnect shows no load on the "speedometer" nor in percent. All firmware is up to date.

I can use both Iphone and Mac to turn the inverter off and on.

Phoenix Inverter
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

7 Answers
mickyritchie avatar image
mickyritchie answered ·

It could just be that your loads are too small to register - that's been my experience with the 12/375.

1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

spirou avatar image spirou commented ·

Same with 12/250. Nothing registers at least until 100W. I asked this same question a while ago. The answer was it's not a precise measurement device.

0 Likes 0 ·
netrange avatar image
netrange answered ·

Phoenix 48/1200 connected to Venus GX with 650W of Load ... But Victron Connect App displays only the colored Ring with "0" Watt.

Firmware is up to date

Somebody with the same problem?

1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Fire Online avatar image Fire Online commented ·
Yes, I'm having the same issues with a 250 and 1200 watts. I pushed them to almost full capacity but it still shows 0%.
0 Likes 0 ·
Alexandra avatar image
Alexandra answered ·

@Netrange

This is a common discussion here on the forums. It is a hardware limitation of the inverter.

We have a phoenix at home with a BMV, usually am more concerned about VA and consumption out the batteries than the load. So have a shunt on it.

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Fire Online avatar image
Fire Online answered ·

I got 3 Phoenix inverters, the 12 | 250, 12 | 1200 did show a load reading until I updated to the v1.30 firmware, now they show 0% load even though I got a load close to their full capacity connected. The white indicator on the scale shows a value but the scale goes up to 200 even though I got a 250 and 1200 watts inverter. On the VRM portal I do see the watts under AC Loads but on the VictronConnect app its all incorrect.
img-0986.jpg

img-0983.jpg



My third inverter is a 24 | 800 and it got the v1.27 firmware, now on the VictronConnect app it says its up-to-date but on the VRM portal it show it needs to be updated to v1.30.

screenshot-2022-09-20-085630.png

screenshot-2022-09-20-090328.png

Also, the scale shows 1600 but its a 800 VA.

Conclusion:
Updating to the v1.3 firmware shows an incorrect scale and 0% load on the VictronConnect app.
I will update the 24 | 800 to v1.3 and post an update of what happens.



2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Fire Online avatar image
Fire Online answered ·

Update on 24 | 800 Phoenix Inverter:
I updated to the v1.3 firmware and it is still working, it is still showing a VA reading. I guess the v1.3 only affect the 12 inverters.

screenshot-2022-09-20-094222.png


2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

peter-3 avatar image
peter-3 answered ·

You are not missing anything getting a value .

under about 40 watts it show zero then jump to 100 watts with 45 watts . ( 28 watt increments )

it is totally non-linear and my 12 volt , 500 av phoenix overloads at 400 watts , so you need to add 200 watts first eg 600 watts before it will take 400 watts .

1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Fire Online avatar image Fire Online commented ·

I'm pulling over 600 watts on this inverter and its still showing 0% load even though the white indicator shows its close to yellow.

screenshot-2022-09-20-094824.png

0 Likes 0 ·
Fra avatar image
Fra answered ·

screenshot-2022-09-22-19-13-00-347-comvictronenerg.jpgFire online Is right.

ITS a firmware bug.

Nothing to do with accuracy of the inverter.

Before the update It shows NORMAL, now shows ever 0.

I have the same problem with 12/375 after some update.

Shame no one is tryng to fix the problem