zuzullo avatar image
zuzullo asked
Do I need an AC Breaker between inverter and appliances?
Our setup is very small. We bought a Multiplus 800 to power 2 AC outlets on the boat. These outlets power one Laptop one coffee machine. :)
Can the 2 AC outlets be connected directly to the inverter AC output? Or do we need to install a circuit breaker between the Inverter and 2 AC outlets?
MultiPlus Quattro Inverter ChargerPhoenix Inverterac out 2
zuzullo answered ·
Right now, (without the Multiplus 800) if equipment is faulty, the breaker at the marina shore power will trip and cut the power.
But yes, I see that adding the MULTIPLUS will require a new breaker between the Multiplus and the 2 outlets.
Do you think we can use this Blue Sea AC pannel https://www.wmjmarine.com/8177.HTML between the Multiplus and the 2 outlets? From what I can see it trips as well in the event of failure on the outlets.
The linked item looks like a circuit breaker and does not have a RCD function. For what you're using it for, I'd second Rob's suggestion that you find a combine MCB & RCD (sometimes called a RCBO). The RCD function adds another layer of safety in the event of equipment failure/insulation damage.
Murray van Graan avatar image
Murray van Graan answered ·
Hi @zuzullo. Yes definitely you would need an RCD - this protects the user from electrical shock and also faulty wiring or equipment. I would also install a circuit breaker after the RCD feeding the AC outlets
Rob Fijn avatar image
Rob Fijn answered ·
Hello @zuzullo, Yes you need both.
You can find breaker with both functions in one. The MCB protect for overcurrent and the RCD is a life-saving device which is designed to prevent you from getting a fatal electric shock if you touch something live, such as a bare wire.
Rob