jackske86 avatar image
jackske86 asked
Multiplus II with Pylontech: DVCC CCL persistently limiting BMS CCL
Hi experts,
Desperately need your support, situation as follows..:
  • Multiplus II, Cerbo GX, 2 x Pylontech US3000C (37A current limit each = 74A)
  • Pylontech parameters correctly visualized (74A): pylontech-paramaters.png
Initially the system was configured according to Victron's tutorial, using "Remote VEConfigure" in the VRM portal. I have been gradually able to upload new configuration files with increasing amperage (1A->5A->35A). Trying to increase/remove this boundary however on the Cerbo's display had NO impact (increase the charge current limit nor disabling the limit, with or without reboot).
What can I do to further increase the limit from 35A->74A, since VEConfigure only allows me to modify this value up to 35A (as seen below)?
AC Charge limit is not constraining (set to 12A), neither should the SOC (59% currently).
Many, many thanks in advance..
Multiplus-IIcerbo gxPylontech
honu avatar image honu commented ·
Multiplus II 3000/35-32 : Guess what is the meaning of the 35 in your device name.
proton avatar image
proton answered ·
Your MP 2 3000 is limited by design to a constant charge of 35A DC if you charge your Pylontechs just from Grid, see the data sheet for it. So, nothing to do.
You can add another DC-chargin source to enhance this, for example some Victron solar chargers.
Bye
prein avatar image
prein answered ·
The multiplus you have is a 35A charger.
So even if the battery allows for more charging current, the multiplus can only do 35A.
So the solution is: replace the multiplus with a bigger one. The 5000 can do 70A