Ricardo Chavarria avatar image
Ricardo Chavarria asked
Energy Meter for a Split-Phase, 125A Service
I got my ESS system installed mid last year and the Grid-Parallel PV system installed this past December. ESS equipment is a Multiplus 48V/300VA/35A with a BYD Battery and a CerboGX. PV system is a Fronius Primo 10k inverter with 8k solar array.
screenshot-2024-01-18-at-113914-am.pngThis is how my system looks, but I'm missing the energy meter.
I'm facing an issue where GX is not counting the generated energy or displaying the topology properly, I'm assuming because I'm missing an Energy Meter. I bought a Victron VM-3P75CT, but to my surprise, the clamps are too small to fit over my 14mm phase wires.
screenshot-2024-01-18-at-114814-am.pngVictron Portal display of my system topology, which is wrong as my PV inverter is actually in parallel with the grid.
img-4397.jpegMain panel on the right with 14mm split-phase wires (large black wires, 120V per phase). Panel on the left is for critical loads, managed by the Multiplus/ESS.
I want to be able to properly count my energy consumption, which is why I'm asking for help in figuring out what meter I should use. From my research, I believe the Victron/Carlo Gavazzi ET340 is the right choice, but I'm afraid the phase wires won't fit into the meter as they're 14mm (13.75mm to be exact) in diameter, and they seem VERY large for any of the Energy Meters I've seen.
Any help would be greatly appreciated. I'm located in Panama. Our grid is similar to the US grid where we have two-phase, 120V per phase.
ESSEnergy MeterFroniusgrid parallel
Ricardo Chavarria answered ·
I want to leave this answer here for posterity.
The proper way to get SplitPhase (L1+L2) reading on a Victron + Fronius ESS is the following:
  1. Purchase an Energy Meter that's right for your application - probably an EM530 or EM540.
  2. Connect things properly
  3. Make sure Energy Meter is showing up on Cerbo
    1. Configured as a Multi-Phase Grid Meter
  4. Modify your Fronius PV Inverter so it uses the sunspec API. This is a CRUCIAL step.
    1. Follow instructions here https://www.victronenergy.com/live/ac_coupling:fronius
    2. And here https://www.youtube.com/watch?v=TWbHn-AAWqE&ab_channel=FroniusSolarEnergy
  5. Make sure you set your PV Inverter to be Split-Phase (L1+L2)
You should now see the Inverter handled properly.
1716866359385.pngNote the Two phases showing up on the Grid Meter AND Fronius PV Inverter
Adding this diagram from the ET340 manual (specifically ET340-DINAV23XS1X), which is how I plan to install it if the cable inputs can support my 14mm cable diameter:
prein avatar image
prein answered ·
first: configure the PV inverter to be connected to AC-In instead of AC-out:
in your GX device, select the inverter and set it to AC-in in the settings.
Ricardo Chavarria avatar image Ricardo Chavarria commented ·
Thanks, thats how I have it setup, but it's not showing up properly. If I change the phase to be Split Phase, it will disappear from Victron Portal.
My main problem is on the physical side, with the missing energy meter and the clamps that won't fit over my phase wires.
prein avatar image
prein answered ·
Probably you can use another current sensor. From this specsheet, you should be able to choose the c/ct1216 as well. But the meter is for max 80A loads. So make sure to first contact victron about this..
https://nl.mouser.com/datasheet/2/447/KEM_SE0204_C_CT-3316988.pdf
Let's see what Victron says about this. Their instructions mention nothing about other CTs, other than saying that if they require replacement, they need to be recalibrated to the Energy Meter, which is a bummer if so...
Thanks!