Fuse blows when Lynx Dist powered. Why?!

When I turn on (close) the battery disconnect to power the lynx distributor the 125A 48V (Victron) fuse blows on the battery connection In the Lynx. The only thing connected to the bus bars on the lynx distributor distributor is the inverter and the batteries. I checked and rechecked polarity and everything is correct. The 48v batteries are reading 53V. The inverter is off. A smart shunt if correctly installed between the bat negative and the negative bus bar on the distributor. The shunt bat plus and aux cables are connected to the bat pos terminal and the mid point positive. As far as I can tell everything is connected properly and secure and there is no reverse polarity. What would cause the fuse to blow When the Disconnect is closed (on) and the distributor is powered?

Multiplus-IIbatteryfuseslynx shuntbusbar
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
seb71 avatar image
seb71 answered ·

What happens if you disconnect the inverter wires from Lynx Distributor and only then you connect the battery to the Lynx Distributor (close the switch)? Also remove all the positive wires from the SmartShunt, just in case. And check for any short between the positive and negative busbars (like a piece of wire). The Lynx fuse still blows or not?

-------

Try to precharge the inverter capacitors, before connecting it to the battery (before turning on the disconnect switch). You can use an incandescent light bulb or a resistor for that.

2 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

duswami avatar image duswami commented ·
Well I thought about trying that , that would entail blowing another $30 victron fuse :/ Before I try that. Any other thoughts? The battery is obviously 'capable' of more than 125a... being 200ah and a 48v system I calculated 107.60A as being the wire/fuse rating Making a 125a fuse even slightly over-sized, but using 1/0 wire..


Incidentally, the next fuse found the bus bar, inverter fuse, did not blow.

0 Likes 0 ·
duswami avatar image duswami commented ·

I found the short! It WAS at the inverter. There was an infinitesimal bit of solder between the battery terminals bridging the connection. Like a hair thick and maybe 2mm long. Wow... thanks for the help.