BoKl avatar image
BoKl asked
REC BMS / CCGX / Multi Plus12/3000/120 settings
I try to setup a LiFePo4 ( Winston ) 12v/400Ah block with Multi Plus and REC BMS ( ABMS Victron compatible). BMS is installed correct, connected to CCGX via CAN Bus. CCGX Can Bus Profile is set to VE.Can & CAN-bus BMS (250 kbit/s) seems to work correct.
Multi Plus is connected to CCGX via VEBus and is also visible in CCGX
I now tried to set up the multi with the MK3 interface. Charger settings are done. My problem is when I chose LiFePo Battery in the config software, I am asked to load and activate an "assistent" knows someone here what the exact setting is?
CCGX Color ControlBMScharger
boekel avatar image
boekel answered ·
Hi Bodo,
As you already found out:
You don't need assistants for the REC-bms, as it is CANbus connected to the CCGX.
You need to use DVCC in the CCGX (and set the REC bms as battery monitor) then the Multi uses the parameters sent by the BMS
Please check al parameters sent by the BMS to make sure setup is correctly done.
Paul B avatar image
Paul B answered ·
You set this up under assistants
boekel avatar image boekel ♦ commented ·
This is not for CANbus bms
drmi avatar image
drmi answered ·
REC-BMS is Victron-compatible (See http://www.rec-bms.com/datasheet/UserManual_REC_Victron_BMS.pdf ). Which settings (Assistent ESS or another?) should be done in VE.Config?
you don't need ESS assistant, unless if you want to feed back power into to the grid.
Paul B avatar image
Paul B answered ·
Its best that you read all the information about the ESS
https://www.victronenergy.com/live/ess:design-installation-manual
but I would recommend that you ask your local agent to help you set this up
He never mentions using ESS, and he doesn't need to / and when it's a mobile or off-grid (van / boat / cabin) installation he -really- shouldn't use ESS
BoKl avatar image
BoKl answered ·
Hi @Paul B
thx for your fast reply. I installed the assistant ( did already before) but that seems not to be the problem. I got a notificaion in the CCGX that "ABMS assistant is installed configured for a VE.Bus BMS but the VE.Bus BMS is not found"
Do I need to enable the REC BMS ( which is visible in the device list at the CCGX ) for the VE.Bus? It is connected via CAN Bus to the CCGX..
BoKl avatar image
BoKl answered ·
Hi Boekel,
That seems to work ... I just need to update the MultiPlus to rel 422 and should than be able to setup all the components
Thanks a lot
Best regards
Bodo
Afonso Indias Zagalo avatar image
Afonso Indias Zagalo answered ·
Hello
I'm here trying to find some help on a issue with the Multi 12/3000/120, CCGX, MPPT 100/30 and a REC BMS connected by canbuss, after solving a cabling problem ( replacing 70 by 95 sqmmm ) and securing all connections the Multi will charge with no problem with land power, however with the generator it will cut on and off the Multi charge. Having monitoring the voltage and Hertz from generator ( a Isuzu 5 KW ) it seems in the writgh parameters 52Hz and 230VDc on start and keeping it all the time.
Thank you in advance
Lisbon
Hi @Indiaszagalo
Please make a separate topic for this, and in this also describe what kind of system you have (off-grid? ESS? Backup?, ..?)
if you are using ESS, you have a grid code set, this can influence generator acceptance.
please read the manuals on the system you use.
Afonso Indias Zagalo avatar image Afonso Indias Zagalo Daniël Boekel (Victron Energy Staff) ♦♦ commented ·
Thank you BoKl for your repply, it is a boat installation and a steel hull, so I'm still working in some isolation issues and we are waiting for a firmware update on the REC BMS.