larry365 avatar image
larry365 asked
1200w device on Phoenix 800
I am working away for a few weeks and would like to take my Nespresso machine with me. It draws 1200 watts (assumed from label and to be check with meter) for 2.5 minutes. Will be used 3 times per day, 5 days a week for 4 weeks.
My camper is fitted with an 800watt Phoenix
The spec suggests that the inverter will handle 130% load for 30mins, I assume at 12v.
So, my calculations
Max load @ 12v: 66.6 amps - drawing, at 90% efficiency, 74 amps
130% load @ 12v: 86.6 amps - drawing, at 90% efficiency, 96.25 amps
Engine running = 14.4v
So max load is actually 960 watts
Allowing a 130% load of 1,248 watts for up to 30 minutes.
Opinions on this setup please. Are the safety features sufficient to prevent damage regardless of what we think?
Cheers
Side note in case its bothering anyone, the cables used are more than sufficient, as is the alternator, ambient temps 20c and leisure battery sufficient C rating.
Phoenix Inverter
Mike Dorsett avatar image
Mike Dorsett answered ·
Personally, I would not risk this! The overload specification will be subject to ambient temperature. Check the specification again for thermal de-rating.
michelg avatar image
michelg answered ·
Hi, I have a Phoenix 800 and it is not a 800W but a 800VA which brings around 750W when temperature is cold. Usually it can bring around 650W, and consider @24VDC a 32A breaker, I use it to power my house and it goes perfectly. When I use the washing machine, coffee machine (nespresso style), or the air conditionner, I need to switch to the 3KVA inverter (june-september is when I do use it 24/7).
So definetly not a good idea. You can consider making coffee using a manual Wacaco Nespresso machine, or a CONQUECO coffe machine, which can use 12V directly and would solve the issue.
(amazon is your friend).
Michel.