multiplus control inverter via SOC

I have a Multiplus 5000/48V , CCGX display and a DMC

The CCGX generator stop/start function is already in use. Would like to turn off the inverter mode once SOC reaches 45% and re-engage at 50%

What is the best way to achieve this?

MultiPlus Quattro Inverter ChargerCCGX Color ControlSOCDigital Multi Control
10 |3000 characters needed characters left characters exceeded

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
mvader (Victron Energy) avatar image
mvader (Victron Energy) answered ·

Hi @bbe,

there is a setting in VEConfigure for that.


Make sure that first the Multi os updated to recent firmware. That soc setting was added only recently.

1 comment Share
10 |3000 characters needed characters left characters exceeded

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Thanks will try this