question

sijtze-de-boer avatar image
sijtze-de-boer asked

Different voltage between VRM and battery

I have connected the power of a Venus GX on a service battery and also a multiplus. Now I see on the VRM Website (monitor) a voltage of 9.6 Volt but my service battery has 12.5 Volt. Why is there a difference between the VRM monitor and the real voltage of the service battery?

VRMVenus GX - VGXbattery system voltage
1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

seb71 avatar image seb71 commented ·

What is the voltage (measured with a multimeter) at the Multiplus battery wires connectors?

0 Likes 0 ·
3 Answers
sijtze-de-boer avatar image
sijtze-de-boer answered ·

On the Multiplus battery wires connectors the same as on the battery at this moment 12.55 Volt.

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

seb71 avatar image
seb71 answered ·

In Venus GX, if you go to "Settings" and then "System Setup", what you have set for "Battery monitor"?


And do you have DVCC enabled?

13 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

sijtze-de-boer avatar image sijtze-de-boer commented ·

Battery monitor -> automatic

DVCC -> disabled

0 Likes 0 ·
seb71 avatar image seb71 sijtze-de-boer commented ·

You only have the Multiplus and Venus GX, right?

What kind of battery do you have? Lead-acid, LiFePO4 (and if yes, what BMS, if any)?


Edit

Also list the Venus GX and Multiplus firmware versions.

0 Likes 0 ·
sijtze-de-boer avatar image sijtze-de-boer seb71 commented ·

Yes only Multiplus 12/3000/120 and Venus GX with GSM and GPS.

AGM battery no BMS at this moment.

I have a BMV 712 but not connected yet.

0 Likes 0 ·
seb71 avatar image seb71 sijtze-de-boer commented ·

The Multiplus firmware version can be seen via VRM, in Device List (VE Bus System).

You can see the Venus GX firmware version in the menu, or via VRM (Gateway).

0 Likes 0 ·
sijtze-de-boer avatar image sijtze-de-boer seb71 commented ·

Multiplus firmware version is 158 product-ID 2609

Venus GX version v2.63

0 Likes 0 ·
seb71 avatar image seb71 sijtze-de-boer commented ·

Venus GX firmware is the latest, but Multiplus firmware is very old.


You can't activate DVCC with that old firmware version on the Multiplus.

In order to update the Multiplus firmware, you need a MK3-USB interface.

-------

Still, change the "Battery monitor" (in Venus GX) from Automatic to Multiplus. This setting is used for SOC, so it might have no effect for voltage, but it is easy to test. Not sure what Automatic mode is using.

After you install the BMV, make sure you set "Battery monitor" to it.

0 Likes 0 ·
sijtze-de-boer avatar image sijtze-de-boer seb71 commented ·

Thank you for now I will try with BMV 712 and newer firmware.

0 Likes 0 ·
seb71 avatar image seb71 sijtze-de-boer commented ·

In that case, make sure to enable DVCC (and SVS + SCS in it).

0 Likes 0 ·
sijtze-de-boer avatar image sijtze-de-boer seb71 commented ·

I have tried VictronConnect but did not work.

Now I will use VEFlash which firmware should I use at this moment the Multiplus is product-id 2609 en version 158 reading out with the Venus GX.

0 Likes 0 ·
seb71 avatar image seb71 sijtze-de-boer commented ·
I have tried VictronConnect but did not work.

Can you give more details?


The latest firmware is 481 (so 2609481.vff for your Multiplus).

0 Likes 0 ·
sijtze-de-boer avatar image sijtze-de-boer seb71 commented ·

Software VictronConnect gives the answer:

Firmware-versie wordt niet ondersteund. Gebruik VEFlash om te updaten naar versie 200 of hoger.

0 Likes 0 ·
Matthias Lange - DE avatar image Matthias Lange - DE ♦ sijtze-de-boer commented ·

The current FW is to old for VictronConnect, so you have to use VEflash.

0 Likes 0 ·
Show more comments
sijtze-de-boer avatar image
sijtze-de-boer answered ·

After firmware upgrade to 2609481 and connecting BMV monitor on the Venus GX everything works very nice.

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.