bathnm avatar image

Smart Solar MPPT 150/70 VE.CAN

I am about to install the above model into my system comprising a Cerbo and Smart Lithium Batteries with a VE.Bus BMS. I have been reading the manual in preparation and found the following regarding the BMS connection.

I am surprised that it suggest the VE.Bus BMS charge disconnect is connected to the L-Pin. The VE.Bus BMS will supply a high signal until a charge disconnect event occurs when the signal will drop too floating. In all other devices the VE.Bus BMS is therefore connected to the H-Pin. Even the description of the use of the L and H terminal match that in all other manual, and implies it should be connected to the H pin.

Could someone advise if this is a typo in the manual and the VE.Bus BMS should indeed be connected to the H Pin of the Smart Solar MPPT 150/70 VE.Can?

Many Thanks


BMSsmart solar set-up helpVE.Can
2 |3000 characters needed characters left characters exceeded

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
Matthias Lange - DE avatar image
Matthias Lange - DE answered ·

It is a typo. I forwarded it to the devs. Thank you for the hint.