I've been unable to find clear information on how to correctly connect the BMS load disconnect to the Phoenix 12/1200. Special cable or just a connection to the right or left remote socket on the inverter?
I've been unable to find clear information on how to correctly connect the BMS load disconnect to the Phoenix 12/1200. Special cable or just a connection to the right or left remote socket on the inverter?
Which Phoenix do you have?
https://www.victronenergy.com/inverters/phoenix-inverter-vedirect-250va-800va
or
https://www.victronenergy.com/inverters/phoenix-inverter-compact
The first one can be controlled with a simple wire at the left contact of the remote connector (manual 3.6).
The second one can be connected to the "Multi/Quattro" port of the BMS with a RJ45 cable.
Additional resources still need to be added for this topic
Phoenix Inverter Smart product page
MultiPlus Product page / Quattro Product page
MultiPlus 230V Manual / Quattro 230V Manual