mike-g avatar image
mike-g asked
Error #68 on SmartSolar 100/30
System:
Venus GX FW ver. 2.53
Multiplus 12/2000-80 FW ver. 469
BMV-712 FW ver. 4.03
SmartSolar Charger MPPT 100/30 FW ver. 1.47
BMV and MPPT are connected to Venus GX via VE.Direct
Multiplus connected to Venus via VE.Bus
DVCC enabled
Shared Temperature provided by Multiplus
Shared voltage and current provided by BMV
After a recent firmware update I'm now getting Error #68 Network misconfigured. Documentation on Error #68 says "charger detects multiple conflicting network sources, with the same priority, trying to send the same information to the charger. VE.Can and VE.Direct interfaces have both the same priority level, and BLE (using VE.Smart Networking) has a lower priority."
This appears to be in conflict, as I am using VE.Direct, which has a higher priority over BLE. I am not using VE.Can.
Disconnecting one or the other clears the error, but reduces functionality.
My working assumption on this setup is that SmartNetworking provides temp, voltage and current info to SmartSolar and SmartSolar uses VE.Direct to provide information back to Venus GX. Is this correct? Are they in conflict? If VE.Direct and BLE are at 2 different priorities, why am I getting Error #68?
Thanks.
Bluetootherror
JohnC avatar image JohnC ♦ commented ·
Hi @Mike_G
What does "reduces functionality" mean?
mike-g avatar image mike-g JohnC ♦ commented ·
@JohnC, my understanding, which is admittedly incomplete, is that if I connect the MPPT with Bluetooth, DVCC can send current and voltage from the BMV to the MPPT. However, no data from the MPPT is sent to VRM through the Venus GX. If I connect the MPPT via VE.Connect, the MPPT will use temperature from the Multiplus and and send solar data through the Venus to VRM but I lose the voltage and current from the BMV. I invite others to correct me as needed.
JohnC avatar image JohnC ♦ mike-g commented ·
@Mike_G
That's not my understanding, but I wouldn't be running two parallel data links and expecting to be able to concurrently select what I might consider to be the best features of both.
I'd pull the BLE link, and revisit the DVCC section of the manual (section 4, STS, SVS & SCS especially): https://www.victronenergy.com/live/ccgx:start
No doubt I'm missing what your expectations really are, but the cause of your #68 issue is obviously the doubled-up data links.
nebulight avatar image
nebulight answered ·
Do you have a smart network between your BMV and your mppt? If so, turn that off and only use DVCC. I got that error message when I had smart networking turned on AND DVCC turned on. You don't need smart networking between the bmv and the mppt as DVCC handles that with your GX.
Hi @Mike_G
you have to choose ;)
Shared Temperature (and voltage) provided by Multiplus
or
for lead-acid batteries, temperature is most important, so I'd choose that. also voltage reading at multiplus is usually good for MPPT's production.
if you don't want the error: disable DVCC
mike-g avatar image
mike-g answered ·
Sigh. The Multi is not ideally located to provide voltage, thus the BMV has to do the job. Is there a roadmap for better integration here?
Hi @Mike_G
No, a the solution could be to have temperature provided by a BMV 702 / 712.
mike-g avatar image
mike-g answered ·
@Daniël Boekel (Victron Energy Staff), do you mean a second BMV? I'm not sure if I'm intrigued or appalled.
I'm saying connect a temperature sensor to your BMV (smart network), or use the Multi's values. (DVCC)
mike-g avatar image mike-g Daniël Boekel (Victron Energy Staff) ♦♦ commented ·
If I'm using the voltage and current on the BMV for start and house, I'm out of inputs for temperature. May have to rethink this.
mike-g avatar image
mike-g answered ·
@nebulight, this was the path I took. Thank you. When I initially tried this, the solar controller couldn't be seen in the Venus' display, generating some confusion on my part. After a couple of connect/disconnect/reconnect efforts, the solar charger is showing up in the Venus. I added a temp sensor to the BMV and that is also working.
VictronConnect bluetooth troubleshooting guide