Fuse for AC in on Multiplus 48/5000?

Had a power surge from grid a while back and this then required a new control board to be fitted. This has been done and the inverter side works fine now but when connected to AC power in, this does not register and charge the batteries or switch the inverter side off. There is none of the LED operating on the left side of the unit either? Having looked at documentation it is telling me that it may be a fuse/breaker on the AC in side that needs to be closed, any ideas where?

battery chargingfuses
4 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

kai avatar image kai ♦ commented ·

can you verify with a multimeter that AC is present at the multiplus' AC in terminals?

0 Likes 0 ·
tonyr avatar image tonyr kai ♦ commented ·

Yes I have checked AC input with multimeter and it is present

0 Likes 0 ·
kai avatar image kai ♦ tonyr commented ·

I'm not sure then. There's no integral fuse/breaker that I can see in my MP. I read the entries in the manual referring to fuse/breaker as the external one upstream.

0 Likes 0 ·
Warwick Bruce Chapman avatar image Warwick Bruce Chapman commented ·

What part of the documentation are you referring to?

0 Likes 0 ·
1 Answer
Daniël Boekel (Victron Energy Staff) avatar image
Daniël Boekel (Victron Energy Staff) answered ·

Hi @TonyR

What values are showing when you connect with VictronConnect or Ve.Configure?