What does "System reset" on MultiPlus?

Hello,

Recently a MultiPlus 48/5000, setup as charger-only, threw a "Fault" for unknown reason and was not accepting AC-In. I first saw something like "Error 11 report", but it didn't show anything and I haven't seen it since. However, I couldn't get MultiPlus back charging. Until I found this:

I couldn't find any documentation what this "System reset" actually does, but I did click it and MultiPlus started charging afterwards!

Have I lost any settings by doing this? Or is its sole purpose to get out of these "Faults"? I'd appreciate a write-up of what it actually does :)

BTW, this "Error 11" caught me off-goard. I'm just using this MultiPlus as a Charger, so I'm bumped why it threw any error at all... Maybe someone knows how to configure it to be more resilient and robust?

Thank you!!

MultiPlus Quattro Inverter Chargercharging batterygx
system-reset.png (51.9 KiB)
10 |3000 characters needed characters left characters exceeded

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
mvader (Victron Energy) avatar image

Hi, it restarts it; clearing any persistent errors (such as an already retried and unrecoverable overload error)


just like switching it off and on again from the main rocker switch on the front.

1 comment Share
10 |3000 characters needed characters left characters exceeded

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Great to know, thanks!!