Mysticmoer avatar image
No Neutral Earth Bond Phoenix 24/800 Inverter
HI. I bought an Victron Phoenix Inverter 24/800 and none of the manuals that come with the inverter or that I can download, shows where I can bond neutral to earth.
The only way that I can see how to do it, is to move internal earth wire to neutral on output board. Would this be acceptable to do as it looks like there is provision made for it do be done.
I have attached some pics of output board.
Thanks
victron products
Hi @Mysticmoer
You are correct, the manual is incorrect, this is on the list to update...
So you'll have to make the N-E connection outside the unit unfortunately.
1 comment Share
Downloaded manual page 13:
1 comment Share
I have also downloaded this manual and there are no circuits or boards with those labels inside.