I have a Victron BlueSolar MPPT 75/10 Charge Controller and am connected to the serial console and am having trouble figuring out exactly what the output means. I have looked at various documents and posts but none seem to match the output I am seeing:
PID 0xA04C
FW 116
SER# HQ1803BV4I4
V 12600
I -150
VPV 15060
PPV 1
CS 3
ERR 0
LOAD ON
IL 200
H19 0
H20 0
H21 20
H22 0
H23 0
HSDS 0
I am guessing V is the battery voltage and VPV is the voltage on the solar panel but I am unsure about the rest. Is I the panel current or the battery current? If its negative does that mean that the load is pulling -150 mA from the battery? What are all the H#s?
Any guidance is appreciated! Thank you.
MPPT ControllersVE.Direct
moved over to the modifications space
whfarms avatar image whfarms Guy Stewart (Victron Community Manager) ♦♦ commented ·
How did you connect to the serial console?
bitpro avatar image
bitpro answered ·
This is what I found about the output:
PID 0xA043 -- Product ID for BlueSolar MPPT 100/15
FW 119 -- Firmware version of controller, v1.19
SER# HQXXXXXXXXX -- Serial number
V 13790 -- Battery voltage, mV
I -10 -- Battery current, mA
VPV 15950 -- Panel voltage, mV
PPV 0 -- Panel power, W
CS 5 -- Charge state, 0 to 9
ERR 0 -- Error code, 0 to 119
LOAD ON -- Load output state, ON/OFF
IL 0 -- Load current, mA
H19 0 -- Yield total, kWh
H20 0 -- Yield today, kWh
H21 397 -- Maximum power today, W
H22 0 -- Yield yesterday, kWh
H23 0 -- Maximum power yesterday, W
HSDS 0 -- Day sequence number, 0 to 365
Checksum l:A0002000148 -- Message checksum
loxley avatar image
loxley answered ·
This is the best documentation I could find on the serial output of the various devices, using the ve.direct protocol:
https://www.sv-zanshin.com/r/manuals/victron-ve-direct-protocol.pdf
Of particular note are the entries that correspond to the "MPPT" column on pages 4 and 5.