Sorry for the poor pics where do I install the shunt in my system?
@Jason Frank You can download the Quick Install Guide here. Diagram 7.
Wiring Unlimited might be useful.
@Jason Frank A couple of safety concerns.
As per battery label, battery produces explosive gas. Make sure that box is ventilated.
Is that a light built into the top edge of the box? Good ignition source for those explosive gasses.
Battery fusing is not optional. The striped cable also needs a fuse.
Red cable at the 12v terminal needs fusing. (If you are running a 12v load on that, you will damage the battery, best to use a 24 > 12 converter)
Your clamps you have used to parallel the batteries is ordinary, also needs to be insulated to prevent accidental shorts.
Agree with the comments about this installation. In addition the batteries need to be clamped down.
Smart shunt goes in the battery negative. To do this you need to join the left battery poles together, connect the battery side of the shunt to the joined cables. All other negative connections must be moved from the batteries and go to the load/system side of the shunt.
Shunt positive goes to battery positive.
But this installation needs professional attention.
53 People are following this question.