Why is my system frequently in passthru?

2 units of Quattro 15kva =30kva with another of 4 nos of smart-solar 250/100 with an additional 75kwh open loop communication (generic lithium, no CAN PORT connection).

what can I do to eliminate the frequent passthru mode?

whatsapp-image-2023-12-05-at-83908-pm.jpeg


CCGX Color ControlVE.Bus Smart Dongle
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

8 Answers
Jason - UK avatar image
Jason - UK answered ·

@fasami oluwaseun Several questions.....

Do you have a grid meter fitted?

Do you have anything connected to the AUX connections?

Are you using an ESS assistant?

Do you have any manual overrides set?1701811288667.png

Do you have an export of your VE Configure settings you can share?



1701811288667.png (36.6 KiB)
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

fasami-oluwaseun avatar image
fasami-oluwaseun answered ·

Do you have a grid meter fitted? NO

Do you have anything connected to the AUX connections? NO

Are you using an ESS assistant? YES

Do you have any manual overrides set? NO

how do I go about this?

I don't have the export of your VE Configure settings.

is it acceptable to share the link to the site with you?


2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Jason - UK avatar image
Jason - UK answered ·

@fasami oluwaseun

1701814234950.png

For example, I have attached a copy of mine.

Example settings.TXT

Any links you share should be read only information.


1701814234950.png (146.0 KiB)
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

fasami-oluwaseun avatar image
fasami-oluwaseun answered ·

kindly find the export of my VE Configure setting

agm 01.PNGagm002.PNG


agm-01.png (23.7 KiB)
agm002.png (18.1 KiB)
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

fasami-oluwaseun avatar image
fasami-oluwaseun answered ·

TAB: General

System frequency 50Hz

Shore current 50.0 A

Overruled by remote checked

Secondary input shore current 16.0 A

Overruled by remote checked

Dynamic current limiter checked

State of charge when Bulk finished 95.0 %

Battery capacity 1750 Ah

Charge efficiency 0.95

TAB: Grid

Country / grid code standard None: (feeding energy from DC to grid not allowed)

Accept wide input frequency range (45-65 Hz) checked

AC low switch mains off 180 V

AC low switch mains on 187 V

AC high switch mains on 265 V

AC high switch mains off 270 V

UPS function checked

TAB: Inverter

PowerAssist unchecked

Inverter output voltage 230 V

Ground relay checked

Inverter DC shut-down voltage 50.50 V

Inverter DC restart voltage 52.50 V

Low DC alarm level 52.00 V

Do not restart after short-circuit (VDE 2510-2 safety) unchecked

enable AES unchecked

TAB: Charger

Enable charger checked

Weak AC input checked

Stop after excessive bulk checked

Lithium batteries checked

Disable VSense (for diagnostic purposes) unchecked

Configured for VE.Bus BMS unchecked

Charge curve Fixed

Absorption voltage 55.20 V

Float voltage 55.00 V

Charge current 100 A

Repeated absorption time 1.00 Hr

Repeated absorption interval 7.00 Days

Absorption time 1 Hr

TAB: Virtual switch

TAB: Usage

Virtual switch usage Do not use VS

TAB: Assistants

TAB: Assistant Configuration

generator start and stop (size:186)

*) Use the general flag

*) Open relay to start generator.

*) Start generator when DC input voltage

is lower than 52.50 volt for 30 seconds.

*) Stop generator when DC input voltage

is higher than 54.00 for 120 seconds.

*) The generator is not stopped by AC input.


general flag user (size:5)

*) Use general flag to ignore AC input 1



Total size of all assistants including the required

(hidden) system assistants is: 260


2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Jason - UK avatar image
Jason - UK answered ·

@fasami oluwaseun You mentioned you have a ESS assistant set up but am I correct in saying you are connected to a generator, or is that just a profile you have set up to avoid polling from the grid with a contactor? I do not see your ESS assistant settings in the above.
In your settings, you have 'Inverter DC restart voltage 52.50 V' but your bettery is 52.4v therefore your inverter will not operate with the current battery voltage and the settings you have. IF the PV is not charging the batteries, and you have no charge settings to the betteries, your Multiplus will be stuck in 'passthru'.

1701856584484.png


1701856584484.png (199.0 KiB)
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

fasami-oluwaseun avatar image
fasami-oluwaseun answered ·

we set the ESS assistance at the initial stage but on the occurrence of the pass-thru mode, we had to override by unchecking the ESS.

Yes, set the inverter DC restart voltage to 52.50v but the diffident levels of battery voltage like 52.6,52.7, etc the pass-thru keeps occurring.

PLEASE...kindly guide me on what to do based on this info and export report of my VE Configure setting.

even, I also experienced pass-thru today again. am worried about this?

kindly find the screenshot of today's event.

I NEED TO RESOLVE THIS PROBLEM ....PLS GUIDE ME.

agm 0004.jpeg


agm-0004.jpeg (28.9 KiB)
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

fasami-oluwaseun avatar image
fasami-oluwaseun answered ·

agm-0004.jpeg (28.9 KiB)
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Related Resources

CCGX Product Manual

CCGX Product page

Additional resources still need to be added for this topic