TAB: General System frequency 50Hz Shore current 50.0 A Overruled by remote checked Dynamic current limiter unchecked External current sensor connected (see manual) unchecked State of charge when Bulk finished 96.0 % Battery capacity 474 Ah Charge efficiency 1.00 TAB: Grid Country / grid code standard UK: G98/1 Amendment 6, G99/1 Amendment 8 AC input 1 Above selected gridcode plus LOM B (compliant) start P(f) at 50.40 Hz start delay for p(F) 0.08 s Droop for p(F) 10.0 % Use Aux1 (if available) as disable FeedIn signal unchecked Reactive power regulation Use a fixed Cos Phi Filter time for reactive power 3.3 s Cos phi at point 1 1.00 TAB: Inverter PowerAssist unchecked Inverter output voltage 232 V Inverter DC shut-down voltage 37.20 V Inverter DC restart voltage 41.20 V Low DC alarm level 30.00 V Do not restart after short-circuit (VDE 2510-2 safety) unchecked enable AES unchecked TAB: Charger Enable charger checked Weak AC input unchecked Stop after excessive bulk unchecked Lithium batteries checked Disable VSense (for diagnostic purposes) unchecked Configured for VE.Bus BMS unchecked Charge curve Fixed Absorption voltage 50.35 V Float voltage 50.30 V Charge current 70 A Repeated absorption time 1.00 Hr Repeated absorption interval 1.00 Days Absorption time 8 Hr Stop charger below 5.0 deg C TAB: Virtual switch TAB: Usage Virtual switch usage Do not use VS TAB: Assistants TAB: Assistant Configuration ESS (Energy Storage System) (size:1761) *) System uses LiFePo4 with other type BMS (This can be either a BMS connected via CAN bus or a BMS system in which the batteries are protected from high/low cell voltages by external equipment.) *) The battery capacity of the system is 474 Ah. *) Sustain voltage 36.00 V. *) Cut off voltage for a discharge current of: 0.005 C= 36.00 V 0.25 C= 36.00 V 0.7 C= 36.00 V 2 C= 36.00 V *) Inverting is allowed again when voltage rises 5.20 V above cut-off(0). *) The solar converter will start reducing its output power at 50.20 Hz. Output power will be reduced to minimum when the frequency is 51.20 Hz. The converter will disconnect when the frequency is higher than 51.50 Hz. *) Total installed PV inverter power is 6000 Watts. Total installed PV panel power is 5000 Watts. *) Relevant VEConfigure settings: - Battery capacity 474 Ah. - PowerAssist unchecked - Lithium batteries checked - Dynamic current limiter unchecked - Storage mode unchecked AC Current sensor (size:186) *) Sensor is connected to auxiliary input 2 *) power rating 7K (dipswitches 1, 2 && 3 on) *) PV inverter coupled on AC output of this phase Total size of all assistants including the required (hidden) system assistants is: 2022 TAB: Advanced limit internal charger to prioritize other energy sources unchecked