Can my ESS produce reactive power to the grid?

I have a ESS with two Quattro and solar power. I have feed in excess power enabled.

This has been operating for two full months and the house meter has

  1. 941 kWh Total Active energy consumed (from grid)
  2. 600 kWh Total Actve enery fed (to the grid)
  3. 40 kVARh Total reactive energy consumed
  4. 330 kVARh Total reactive energy fed

I can understand some consumption of reactive power due to some pump motors we have, but not the export of reactive power.

Any help on this is much appreciated.


ESSgridpower meter
2 comments
2 |3000 characters needed characters left characters exceeded

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Hi

Not sure if the invertor can export reactive power, its charger has a power factor of 1, is all it says in the technical specs.

Depending on the grid code setting requirements. Need to ask victron technical engineers

as it is not mention any where in there manuals at all?

Normally they are set to a range of .8 to 1 unity PF, most modern grid tied inverters do.

Not sure on these Victron units.

If you want to lower your kVAr demand fit power factor correction capacitors across your motors, this will make your system much more efficient and save your power consumption.\ even more.

So you must have a smart meter depending on your power company, they will bill you extra kVAr demand charge as well as kW charge, depending on the country your are in and the power companies policy.

If you want to know what size capactors to fit across your motors, i will need the voltage

and current rating, HP, Kw or the name plate ratings from the motor, so i can calculate it for you if required.

Unless you are billed on a kVA demand one would not want to generate kVAr’s. All the active energy is in the kW’s. So with unity power factor all the amps is going toward kW.

kVAr is called apparent energy, it creates higher amps without doing any work.

1 Answer
Johannes Boonstra (Victron Energy Staff) avatar image
Johannes Boonstra (Victron Energy Staff) answered ·

Correct, an inverter cannot send reactive power to the grid and will try to be powerfactor 1 at all times.

1 comment
2 |3000 characters needed characters left characters exceeded

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Thanks Johannes. Is there a setting that allows a power factor range or Victron Quattro Inverter/chargers are always working as you mention?