in my three-phase-system (3x Multiplus II 48/3000) one single Multiplus (L2 phase) stopped working last night. Instantly after powering on this Multiplus, LED indicators "bulk", "absorption" and "float" start flashing. The other two Multiplus switch to Startup-State.
Searching for a hint in documentation and this forum I still don't have a clue how to fix this.
As the three-phase-system worked for about 10 months now without changing a thing I wonder what caused this error and how to fix it?
Appreciating your comments!
Cheers, Peter
Multiplus-IIerror
peterepeat answered ·
My dealer sugested to re-install the Firmware using VE.Flash (and not Victron Connect) and it worked. The error is gone, my three-phase-system is working again.
seb71 avatar image
seb71 answered ·
Acording to the Victron Toolkit phone app, that LED sequence means "Hardware or EEPROM error":
Note: These three LEDs also blink during programming of the assistants with VEConfigure3. There is no error in that case.
If all other cases this indicates an error and the system will be off. The reason is one of the following:
Typically occurs when firmware has been updated with an older version of VEFlash. To recover, see the VEConfigure3 requirements PDF .
Can also occur during startup when data in the EEPROM is corrupted. In some cases this can be solved by connecting to VEConfigure.
In case this error appeared at random (not directly after a firmware update) and cannot be 'repaired' with VEConfigure there is a hardware or calibration error. Contact Victron service.
Thank you @Seb71 for your comment
I connected using "VE Bus System Configurator" showing this error information, only on L2 inverter:
The system cabeling worked for months. As the three inverters are daisy chained and the last inverter L3 does not show an error, the interface cabeling for the middle inverter L2 can not be so bad, can it?
"Victron Connect" showed the same error #10 as "VE Bus System Configurator" did.
"VE Configure 3" does not show an error at all:
You can try to reset the unit to stand-alone but I guess you have to contact your dealer for warranty.