Victron Multiplus 12/1600/70

maybe I'm not seeing it right, but a direct question to Victron is not an option.

I am experimenting at home with various mppt inverters and now want to continue with the multiplus. my question is : can the Victron Multiplus 12/1600/70 also feed back into the grid

victron products
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

2 Answers
Alexandra avatar image
Alexandra answered ·

@Paul

Yes, it is able to do so with the right programming.

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Paul avatar image
Paul answered ·

thank you , time to replace my current inverter.


2 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

ejrossouw avatar image ejrossouw commented ·
Depending on where in the world you plan on using it and your local rules and regulations, be mindful that it may not be certified/type tested to be used in this way on your local grid. Also, it lacks dual redundant relays, which is a requirement by most grid operators for grid synchronous operation.
0 Likes 0 ·
kevgermany avatar image kevgermany ♦♦ commented ·
Also you need a GX device if there isn't one built in to the selected model.
0 Likes 0 ·