roachmon avatar image
roachmon asked
Possible to combine x3 shore power inlets for ~90A?
A customer had this question about a possible system for a van running a chemlab/test equipment. Ideally, when the opportunity is there, they would like to charge the batteries as quickly as possible via shore power.
The system:
Quatro 48v/8000
x2 Smart Lithium 25v batteries in series
AC-in 1 shore power
AC-in 2 generator
Is it possible to have 3 shore power inlets combine before entering the Quatro? The idea would be to have each shore power cord plugged into a different outlet (each on its own breaker). Each cord would be able to bring in ~20-30A totaling ~90A of 120V charging.
Is this possible? Would the 'combining' of circuits cause the outlet circuits to trip their breakers?
MultiPlus Quattro Inverter Chargerbattery chargingshorepower
snoobler avatar image
snoobler answered ·
Only if the three outlets are in phase and on separate supply circuits.
Even then, I would not expect that each source would stay within it's 15-20A limit. extension cord gauge/length (resistance) and the outlet wiring itself (can't control that) would influence how power is drawn from each outlet.
I think a better solution would be a separate charger - specifically the EG4 Chargeverter. it can operate on either 120V or 240V (will require a custom adapter) and supply 50A @ 120v input and 100A @ 240V output with adjustable current and absorption voltage. On a 15A circuit, it would be limited to ~30A.