Image CaptionI’ve installed my Smart Shunt 500 and setup it up for 2 200Ah lithium batteries in parallel.
These are the settings:
The system isn’t showing any current or power usage with some light loads.
What have I done incorrectly?
Image CaptionI’ve installed my Smart Shunt 500 and setup it up for 2 200Ah lithium batteries in parallel.
These are the settings:
The system isn’t showing any current or power usage with some light loads.
What have I done incorrectly?
Here is the status page
Usual problem is it's wired wrongly.
There should only be the shunt battery side connected to the battery negative. All previous connections to there must be moved to the load side of the shunt. No exceptions, especially the battery earth/ground connections.