question

jimhon avatar image
jimhon asked

correct mcb ac out 1 and 2 for multiplus 48 5000 70

Can anyone give me the correct size of mcb for ac1 out and ac2 out and how its worked out. Thanks in advance

victron products
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

2 Answers
wkirby avatar image
wkirby answered ·

This depends upon what size of cable you plan to use.
The MCB will protect the cable.

1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

jimhon avatar image jimhon commented ·

Cable size is 10mm. I am on the understanding how it is worked out by 5000/ 230v = 21.7a . Is this correct?

0 Likes 0 ·
JohnC avatar image
JohnC answered ·

Hi @Jimhon

You also need to consider that the Multi has ACIn to passthrough as well as it's own output. In the 5kVA EasySolar box (Multi I with breakers), Victron provide a 63A RCD for ACOut1, which is then split off to 10 and 16A mcbs for individual circuits. ACOut2 just has a single 16A mcb.

These could be easily changed out to something else, or the wiring changed around to have more mcbs on ACOut2. All within good practice of course.

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Related Resources