I am troubleshooting a 3 phase system for a client - 3 x Quattro setup as 3 phase.
3 Phase generator is connected to AC In 1
Site/Shore Power is connected to AC IN 2
The site power works great, but it won't seem to accept the generator input. (I don't have both connected at the same time, btw)
I haven't tried swapping the inputs over yet.
I have tried turning on Dirty AC, turning UPS off and turning off switch as a group.
The relay clicks and then nothing happens, as if it tries to connect and then decides not to... any suggestions?
MultiPlus Quattro Inverter ChargerGenerator3 phase
JohnC avatar image
JohnC answered ·
Hi @DBX120
There's some suggestions here.. https://www.victronenergy.com/live/multiplus_faq
Start with a low Input Current Limit and work up when you get it to accept. Also, you can try it, but treat WeakAC as a last resort, there may be something else wrong if you absolutely need that.
Marc Heymans avatar image
Marc Heymans answered ·
Check the following,
Voltage input of the generator
Frequency of the generator
Make sure both of these are within the parameters set up in the inverter tab of VE configure
mjs500 avatar image
mjs500 answered ·
stupid question have you made shore generator phase rotation is same as Site/Shore Power in but looking at date first post id hope its fix by now