bbossyns avatar image
bbossyns asked
EM330 - EM340 in 3x230VAC grid wrong readout
We installed an energy meter EM340 (in-line) grid meter and in another application an EM330 with current clamps. We see that if we program the meter to a 3P grid (3x 230VAC and no N), which still exists a lot in Belgium, that the Cerbo Measures 0VAC as line voltage. Therfore the internal calculation of power and consumption is not correct. Could this be a software issue from the Victron side? Because in the meter itself all values are correctly displayed.
Kind regards and thanks for the help.
Energy Metergrid
@BBossyns
Victron does not connect to delta connections.
They needs a neutral connection to work, so not likely able to reference without it.
bbossyns avatar image bbossyns Alexandra ♦ commented ·
Dear Alexandra
Thanks for your answer. We don't put the inverter in 3-phase config, we only use a single phase inverter in this case. The L of the inverter is connected to L1 and the N to L2 or L3.
What we would like to obtain is the phase-compensation regulation of Victron in this configuration, because this could help us store the PV-inverter energy which is somtimes connected to a different phase or phases.
So we would like to know if there is anything to be done about the wrong read-out of the values from the Energy meter itself.
Thanks and kind regards
tokke avatar image tokke bbossyns commented ·
Going to follow this as I'm design my system in the same setup (3x230V, no neutral, single phase ESS)
Energy Meter Selection Guide