I have a Phoenix Smart Inverter 24/2000 and a VE.Bus BMS.
The inverter doesn't have a VE.Bus connector.
How do I connect these two?
Below the picture with the available connectors.
Do I need an additional cable?
![schermafbeelding-2022-10-13-om-120920.jpg](/storage/attachments/41255-schermafbeelding-2022-10-13-om-120920.jpg)
I have a Phoenix Smart Inverter 24/2000 and a VE.Bus BMS.
The inverter doesn't have a VE.Bus connector.
How do I connect these two?
Below the picture with the available connectors.
Do I need an additional cable?
The VE.Bus BMS has a Load disconnect output. You need to wire this to the Remote H pin on that green connector of the Inverter (don't forget to remove the wire loop).
See also: Remote Connector in the Phoenix manual